K - Factor

K - Factor

K - Factor

(OP)
Could anyone give me any good websites which discusses the K factor (US) or factor K (europe)

RE: K - Factor

I'm not sure of any websites, but, K-factor gives you and idea of how much heat a transformer can take.  For example, a K-4 xfmr can take 4 times as much heat as a standard xfmr, and so on.  As a side note, K-factor doesn't address harmonic mitigation, only heat.

Mike

RE: K - Factor

jstickley

That was an excellent link and I vote a star for you.

RE: K - Factor

(OP)
Thanks for your links,

Jstickley, the K-factor or Factor K I was talking about was to do with transformer derating due to harmonics.

RE: K - Factor

The K-Factor (used for rating transformers for harmonic currents) was has been introduced for marketing purposes in the US and is a very peculiar way to describe how harmonic currents lead to additional heating in a transformer.

Search the IEEE Transactions on Industry Applications for a very intresting dicussion on the origin of K-Factor and the drawbacks of that definition.

In Europe it is not common to use the K-Factor rating.

Two different applications have to be distinguised:

Dedicated converter transformer:
In this case it is common (and recommend by the approbiate IEC-standard) to specify the current harmonics for the most unfavorable operating condition when buying a transformer.

Distribution transfomer:
In this case most people don't worry about harmonics (regarding transformer heating!). I guess the reason is that in Europe the lines are not as much loaded with harmonics as in the US.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources