Acceptable Test Values for new 2KV cable.

Acceptable Test Values for new 2KV cable.

Acceptable Test Values for new 2KV cable.

(OP)
When testing 2kv Cable (unshielded) that will be used in a 900vdc system, what are the acceptable results for a megger test at 2kvdc?  The design engineer calls for a PI as well. One run has a PI of less than 1 but has a ten minute read of 600 Megohms.

RE: Acceptable Test Values for new 2KV cable.

EP,

Our company standards would be a 1kV megger test with a minimum IR of 100 Mohms. It is not a normal test for a PI on a cable and I am not sure why this has been specified. A PI minimum of 2 is for equipment.

Cheers, Coingy

RE: Acceptable Test Values for new 2KV cable.

I would assume that the 900Vdc system is ungrounded so a value of 600mohm would be quite acceptable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources