Acceptable Test Values for new 2KV cable.
Acceptable Test Values for new 2KV cable.
(OP)
When testing 2kv Cable (unshielded) that will be used in a 900vdc system, what are the acceptable results for a megger test at 2kvdc? The design engineer calls for a PI as well. One run has a PI of less than 1 but has a ten minute read of 600 Megohms.






RE: Acceptable Test Values for new 2KV cable.
http://www.gmc-instruments.com/resources/p1/m_5000dpi/db_gb.pdf
for PI
http://www.ecmweb.com/ar/electric_understanding_insulation_resistance/
etc. for more info
RE: Acceptable Test Values for new 2KV cable.
Our company standards would be a 1kV megger test with a minimum IR of 100 Mohms. It is not a normal test for a PI on a cable and I am not sure why this has been specified. A PI minimum of 2 is for equipment.
Cheers, Coingy