Open Delta Transformers

Open Delta Transformers

Open Delta Transformers

(OP)
Could anyone tell me what would be the highest voltage that an open delta transformer's "wild leg" could reach?  I have measured upwards of 350V to ground on a 230V system.  Could this potentially be higher on other systems?

RE: Open Delta Transformers

Are you sure that you have an open delta?
Typically, a wild leg is used to refer to a 3-phase delta system(typically 230-240V phase-to-phase) with one winding center-tapped and grounded. The potential between ground and the two phases of the tapped coil are 1/2 the phase-to-phase voltage, while the potential between ground and the third phase(the wild leg) is higher by a factor of 1.73.

RE: Open Delta Transformers

Hello all,

DanDel is right, in normal operating conditions, the higher phase-to-ground voltage is 1.73 time the lower phase-to-ground voltage for a transformer configuration with mid-tap grounded open delta. See also NEC fig 250-3, art 215-8, 230-56 and 384-3.

In a not normal operating condition, continuous overvoltage on the red-leg delta (wild leg) occasional could occur particularly on unstable open delta system. Some of those possible overvoltages are ungrounded connection, ferroresonance, harmonics, unbalance voltage, etc.

Unfortunately, there is not a cookbook to make a specific recommendation to determine the abnormal conditions. Consider checking first the obvious, transformer connection, balance voltage, regulation, neutral/ground connections, harmonic content, etc.

Good luck

RE: Open Delta Transformers


Will—Look over the transformer-secondary configurations at http://home.att.net/~benmiller/elecsys.htm
It sounds like you are describing a 3ø 3-wire system with no intentional ground connection to the serving transformer-secondary terminals.  As Dan and cuky have suggested for a grounded four-wire delta system, you should not read any more than about 220 volts to ground—or not exceeding 255V for a “corner-grounded” system.  If indeed no terminals on the secondary windings are intentionally connected to ground, it may be possible to read higher-than-normal ø-ø voltage to ground.  This may be a case where there is primary-to-secondary leakage from the transformer-set primary side, which is almost always fed from a higher-voltage source.  Also, a resonant or arcing condition in the 240V system could cause readings greater than nominal ø-ø voltage.  As you might imagine, this can be stressful to electrical insulation on anything connected—with motors and transformers being the most easily damaged.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources