Hi,

We are revamping our clean room areas. We have to monitor the pressures in the rooms and keep them within +/- 5 Pa. What is the preferred method: constant flow valves in in- and output ducts, or use a regulating valve in the outlet duct?


Kindest Regards,

Marco Bakker

RE: constant flow or regulator

Do you mean dampers? Actually modulating type dampers are better option but it all depends upon cost of investment and system response characteristics you required.

Constant flow dampers are cheaper option but they take time to  stabilize once the pressure balancing gets disturbed.

Modulating control dampers should be controlled by a room pressure  transmitter and position of the sensor inside the room is very critical.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources