Single Core High Voltage Power Cables
Could any one please tell me the relationship between positive sequence and zero sequence resistance / reactance for single core HV power cables.
I am looking for this information in connection with distance protection setting calculations for the 33kV Cable distribution feeders.
I tried some cable manufacturers' websites such as Okonite but to no avail. It would be helpful if I can obtain typical values for different size cables.
Thanks in anticipation.
Raghunath
RE: Single Core High Voltage Power Cables
Westinghouse T&D Reference Book.
Siemens Power Cables and Their Application, Part 1.
Rating of Electrical Power Cables, George J. Anders, IEEE Press.
You should be able to get data for particular cables by contacting the manufacturer.
Thanks for the response. I was told by a colleague that the zero sequence impedance would be equal to the positive sequence one. Is he right?
Raghunath
It would not be valid to use the ratio for this example on other cables or spacings.
http://www.kerite.com/catalog/catalogfiles/impedance_data_power.htm
etc. for more info
http://www.ece.utexas.edu/~grady/EE394_Spring99_Test_1.pdf
etc. for a little calculation
The responses from all of you have been quite inforamtive, thanks once again.
Raghunath