Testing an SCR

Testing an SCR

Testing an SCR

(OP)
I had a problem with the SCR module ( 2 in 1 package ) which has a high failure rate in our production. I want to know know what's wrong with this SCR. It is rated 2x130A 1200V. Anybody knows how to test this kind of SCR?

RE: Testing an SCR

I worked in SCR and Triac applications for several years and the biggest problem I encountered was insufficient gate drive which would result in a partial turn on of the junction.  All of the current would crowd into only part of the junction resulting in serious heating and junction failure.  I suggest that you check the gate drive against the manufacturers specification.  You could have insufficient current or insufficient duration of the gate current.

RE: Testing an SCR

Very good point Jim.  Very common failure mode.

RE: Testing an SCR

Oslec,

What is the application?
If you apply this thyristor in the 480 volt, system unless you have a very good snubber circuit it could fail very easily.
You can also check the di/dt of the gate current against the factory specification and make sure the snubber circuit is properly sized.
You can also send the failed devices back to the manufacturer and ask for failure analyses.

RE: Testing an SCR

(OP)
Hi 1x1x1x,
It's being used in a three phase 400V UPS system as part of the bypass circuit.If there's something wrong with the system, the UPS will turn to by-pass mode and the AC will pass thru this SCR and then to the load, thus bypassing the UPS.
 

RE: Testing an SCR

Oslec,


In your application he peak reverse voltage of the thyristor looks OK.
Make sure your snubber circuit is selected properly, and I can recommend an MOV against overvoltages. Also as was suggested earlier by jimthompson, check the gating circuit, make sure that the gate current duration, di/dt and peak value is in the specification. If you continuously gating the thyristor after turn on check with the manufacturer about it. Mostly the cases, the continuous gate current can be dropped after to the smaller value if the thyristor is turned on, and the thyristor current is higher than the latching current.
Still I can recommend to send the failed thyristor for failure analyses it will reveal the root cause of the problem.


RE: Testing an SCR

Another method of failure is a fast dv/dt.
The device specs will tell you the max dv/dt for that device.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources