Nuisance tripping of Air Circuit breaker

Nuisance tripping of Air Circuit breaker

Nuisance tripping of Air Circuit breaker

(OP)
MY main incomer to my building is protected by a 450kva/625A ACB it trips now and again but: there is no averload my max demand is 333kva, there is no fault on any of my circuits and the electricity board is saying that they have not had any problems with the supply voltage on any phase. Is it likely to be a dodgy breaker or could there be another cause. Gratefull for any help

RE: Nuisance tripping of Air Circuit breaker

What's it tripping on?  Overcurrent?  Some other relay?  How old is this -- are the relays electronic or induction disk?  When's the last time the relays were calibrated?  When's the last time the breaker was overhauled?

You need to provide more specifics.  Your question sounds something like:  "My car keeps breaking down.  Any idea why?"

RE: Nuisance tripping of Air Circuit breaker

I once had an Allis-Chalmers 5KV breaker trip for no reason several random times.  It's culprit turned out to be a latching mechanism very much in need of cleaning and lubricating.

RE: Nuisance tripping of Air Circuit breaker

You might what to check for harmonics. Read phase currents and neautral current.

RE: Nuisance tripping of Air Circuit breaker

Don't forget the possibility that it's operating correctly and protecting you against intermittent ground faults or some other problem.

RE: Nuisance tripping of Air Circuit breaker

This is one that you have to watch, firstly the breaker age has to be checked and how often it has been serviced, you also have to consider especially in todays climate just how much loading can be attributed to computer based loads or anything being fed of an inverter drive aircon and building ventilation uses such things nowadays and this can add to the harmonic content and also produce over currents in the neutral line.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources