AWG cable info
AWG cable info
I work for a UK company and we have received some wiring info from the US. The cable size is 2 x 3/0 , which I understand to be 2 of approx 85sqmm cable, but after this they have followed up with 500MCM. Does anyone know what this stands for?
RE: AWG cable info
References:
1. NFPA 70-1999 (National Fire Protection Standard also known as "National Electrical Code (NEC)"
2. Fink D. G., Beaty H. W. "Standard Handbook for Electrical Engineers," 14th Edition, McGraw-Hill Co., 2000, Page 4-20
cmils=in**2 x 1,273,200=mm*2 x 1973.5
k=M=1000
RE: AWG cable info
THe CM in MCM is circular mils. The M may mean Metric, at this I can only guess. Check out neewc.com for info source.
Cheers!
Mark
RE: AWG cable info
MCM=(M=Roman 1000, C=Circular, M=Mils)
RE: AWG cable info
Alpha wire tables give 3/0 as ~ 170kCM and 87 square mm (depends on stranding), so the 500 MCM is 30% high in my books.
Owen
RE: AWG cable info
RE: AWG cable info
TO ANSWER YOUR QUESTION ABOUT AMERICAN WIRE GAUGE CONDUCTOR SIZING.
A 3/0 COPPER CONDUCTOR HAS A CROSS SETIONAL CIRCULAR MIL AREA OF 167,800 CM. IN INCHES THE DIAMETER IS .470IN AND THE CROSS SECTIONAL AREA IS .173SQ IN.
A 500 MCM COPPER CONDUCTOR HAS A CROSS SECTIONAL CIRCULAR MIL AREA OF 500,000 CM OR 500 MCM. IN INCHES THE DIAMETER WOULD BE .813IN. AND THE CROSS SECTIONAL AREA WOULD BE .519SQ IN. I HOPE THIS INFORMATION HELPS.
RE: AWG cable info
Table 4-12 includes 4/0 AWG copper wire with the following data:
Diameter=0.4096 in
Cir mils=167,800
Sq in=0.1318
Table 4-17 includes 500MCM AWG copper cable with the following conductor data:
Diameter=0.811 in
Cir mils=500,000
Sq in=0.3927