How does over compensation affect the bill?
I hope someone will be able to answer my question. What happens to the energy bill if the capacitor bank is over
compensating, ie creating negative vars on one phase. This
is a 3 wire Delta service. Why would a bank overcompensate?
E
E
RE: How does over compensation affect the bill?
The impact on billing depends on the utility's metering setup and your rate tariff. It would only impact the power factor/reactive portion of the bill, not the energy or kw demand.
Older meters probably are not capable of metering reverse power or var flow, so they wouldn't know anything about it. Newer digital meters could register it, but it depends on how the meter is configured as to what happens.
As far as the overcompensation, if it is a fixed bank, that is, it doesn't have steps that close in and out as the reactive load changes, the capacitor bank may be too large for the application. If it is an automatically switched bank with steps, it should be checked out for proper programming and connections, especially if it is overcompensating on only one phase. What type of capacitor system is it? Voltage? kVAR rating?