480 Volt 3 PH Soft Starter By Pass
5
Hi, All
    I just read the 12 or so, different post about soft starters, and I have a different question reguarding the use of these devices.
    We have installed several SMC soft starters over the past six months. They are on a 25 HP motor, 480 volts 3 PH. The 480 volt power system is an ungrounded system. IE the unit sub is a 2500 KVA delta - delta transformer. They had been running OK for several months. The motor FLA is 31, but the normal running load is only about 12 amps. Very lightly loaded.
    Last week, we had several of the soft starters shut down, within seconds of each other. We noticed, that at about the same time we had a single phase ground, coming and going. Several hits every few seconds, lasting for up to 20 min.
    When we looked at the phase to ground voltages, using a Dranetz analyzer, we see transients up to 900 volts, when these grounds occure. Apparently the soft starters don't like the "Noise" on the line, and shut down.
    My plan is to install a 3 PH contactor in parallel with the soft starter, and have it by pass the soft starter aftr the motor is up to speed.
    Question, do I need to size the by pass contactor, based on the motor HP, or can I use a smaller unit, sense it will only see runing current and not starting currents?
The soft starter unit itself, has 3 small relay contacts, used to by pass the SCR's, after the motor gets up to speed.
   The bypass contactor will be used to disconnect the motor from the line when the motor is stopped, and / or when the motor overloads take the motor off line.
Thanks for your response.
RE: 480 Volt 3 PH Soft Starter By Pass
Please search this site for extensive discussion and references on ungrounded and [high] resistance-grounded electrical systems.  Transient-overvoltage problems cannot be fixed with bypass contactors.
busbar
    Thanks. I have read most of the post about ungrounded 480 volt systems. I have studied the subject in great detail and understand the issues with unground systems.
    I have ordered a high resistance grounding system to be installed on this unit sub. However, I have about 40 unit substations, and all are delta - delta. This plant has operated for 60+ years with unground systems.
    It's these new soft starters, that is this weeks problem. I would like to install the HRG system on all of the unit subs, but need the $$$. This problem may now help me get the $$$, as it did for this one substation.
   The by pass contactor will keep the machines runing. As a electrical reliability/power quality engineer, my first need is to keep the production rolling, and second, improve the over all power quality.
   Question; Do you think the HRG unit will clean up the "Noise" to the point I would not need the by pass contactors? I'm not sure it will.
   I have read reports that indicate, by adding the HRG units, the number of motor failures and grounds on the system will go down greatly. Has anyone seen published data of studies on this?
1.  jburn, if I understand your description, ‘bypass’ contactors leave the VFD line-side rectifiers and load-side transistors still exposed to ø-g transients.
2.  High-resistance grounding {and conversions of ungrounded systems} for low-voltage distribution have been discussed in IEEE Transactions on Industry Applications for at least 30 years.  [Old habits die hard, I guess.]  Search on author J P Nelson, for one.
3.  High-resistance grounding is not an absolute panacea, but is so fundamental for low voltage systems that it should be close to the top of the list where ground-overvoltage problems are encountered.  Ungrounded-system problems are well recognized and have been publicized since at least 1955 [Beeman].
4.  Use your “analyzer” for before-and-after comparisons.  Process of elimination.
busbar,
    Thanks. I have worked with ungrounded systems for over 30 years myself, in several different industrial plants. (23 years in this one) I purchased a copy of Beeman's book years ago, and it is well used.
Actually, use of bypass contactors on soft starters is a good idea, even without transient problems.  Some manufacturers (Cutler Hammer, I think) provide bypass contactor as a standard feature.
The soft starter semiconductors have voltage drop and heat loss even when continuously conducting and the bypass contactor eliminates most of this.
If you are installing your own bypass contactors, I think they need to be fully rated for the motor horsepower.  You also have to make sure that you don't bypass your overload protection, obviously.
If you're trying to reduce contactor size/cost, you could go with IEC-rated contactors instead of NEMA.  I wouldn't do it, but it is an option if you have physical space constraints.
Hello jburn
Bypass contactors can be used with soft starters and will provide extra protection to the SCRs against current transients while running and reduce the power dissipated by the starter during run also. Additionally, because the SCRs are shorted during run, they will be cool for the next start. This can sometimes allow a larger motor to be connected to a given starter.
The bypass contactor is only going to carry rated line current and will not be in circuit during start, therefore it does not require any overload capacity. Effectivley, the current carried by the bypass contactor looks like the current carried when controlling a resistive load. An AC1 rated contactor with a thermal current equal to or greater than the rated current of the motor is what is needed as a bypass contactor. This will be smaller that the typical motor rated (AC3) contactor for this motor.
Best regards,
Mark Empson
http://www.lmphotonics.com
dpc & Mark
    Thanks for the replies. You have been a big help. In my case, the SMC I am using has internal bypass contact around the SCRs. The SCRs are not being damaged, the SMC units just drop off line. The additional bypass contactor I plan to install will be used to get the SMC electronic trip circuit out of the picture. The additional bypass contactor will also have a set of motor overloads. The duty cycle for this application is only one start every two or three weeks, or less.
jburn
The only comment I want to add to Marke's is that using a contactor that is rated for Across-The-Line starting gives you the added redundancy of being able to start the motor should the soft starter fail. Compare the extra contactor cost with the cost / hour of downtime of your machine. Otherwise he is correct in selecting the contactor for the running current only. This method is called a Shunt Bypass by the way.
Something you need to consider very carefully. You did not mention which version of SMC is being used. Some include overload protection and some do not. If yours is the kind with OL built in, you will be bypassing the OL when you bypass the soft start. Check it carefully before implementing.
In addition, I am curious as to which SMC you do have. I was not aware of any that include SCR bypass.
Quando Omni Flunkus Moritati
jraef
    Both Allen Bradley, and Cutler Hammer have units with an internal bypass. The AB SMC-3 unit has an internal bypass. The Cutler Hammer models S751, and S801 both have an internal bypass.
Thank you. I know about the CH unit, but I have not yet seen the SMC3.
Jburn,
I am curious as to how you have determined that the transients are what is causing the problem. The SCRs should just be fully gated and the any transient voltage should just be passed through to the motor (not good for the motor maybe but no problem for the SCRs).
I would suspect the problem is related to one of two things. Since the softstarter is on such a lighly loaded motor 12A vs 25A. I suspect that you have the "energy saver/Solid state heater option" on.  If this is the case you may want to try and shut this off. The SMC is looking at PF and may interpet the sudden change caused by the transient as a "Line fault" as described in the AB manual.
The other possiblity revolves around the control power for the softstarters. During the fault the control voltage could be going either high or low. This could also be causing the problem. Try a seperate 120V supply for a while if possible and see what happens, if it solves the problem use a UPS or ther line voltage conditioner on the 120V side
tmahan
    I have a system in place that capatures, time stamps, and stores every ground event in a database, on all of my substations. I can look at the past history of ground activy on any substation. Every time I had an SMC drop off line, I had recorded ground activity on the substation, that the SMC was on. The corralation left no doubt that  was the problem. After the first loss, we installed a Dranetz analyzer, and we recorded the transients on the system, phase to ground, with each ground strike.
Suggestion to jburn (Electrical) Jan 30, 2003 marked ///\\\
busbar
///This is great.\\\
///Please, have you performed high-resistance system grounding calculation? What are the results, e.g. for the ground fault current? What is your cables Insulation Class Level?\\\
///Yes, indeed. Especially, the arcing problem with soft starters being bypassed could make money available very quickly, considering that many motors may burn simultaneously by high overvoltages.\\\
///Yes, however, in very risky operation that you are very well aware of as a reliability/power quality engineer.\\\
///Yes, however, this will be at very high risk to various loads especially to motors.\\\
///Sometimes, risks pay off handsomely.\\\
///HRG does not mitigate harmonics. It only allows one fault to ground for a period of time determined by the cable Insulation Class, 100%, 133%, or 173%.
///Yeas, you are justifiably not sure.\\\
///Yes, especially when voltage Total Harmonic Distortion (THD) is less or equal 5%.\\\
///There have been some articles published in EE Journals, when the ungrounded systems were gradually commuted to grounded systems using system groundings.\\\
Regarding your original posting, I definitely agree with Marke and would recommend fully-rated bypass contactors.  At the very least, this will maximize your uptime by enabling you to easily start motors regardless of whatever other problems you're having with the SMC's.
High-resistance grounding modification could be implemented as a small site-assembled transformer set with a resistor.  This is worth examination towards minimizing drive misoperation.  With in-place monitoring to observe ground-overvoltage incidents, it should not be overlooked.
…very roughly—three 1kVA transformers—2kW resistor—class-J fuse block…
Comments to various posts:
We have a large number of ungrounded Wye 480 volt subs and a number of HRG equipped subs.
Question:
When you say 900 volts on the grounds - is this RMS volts to ground on the ungrouded phases?  I have seen three instances (2 on a HRG Wye and one on a floating Wye) where the phase to ground went above 480 Volts to ground.  In all cases the fault was a inductance limited ground fault downstream of a 480V lighting ballast.  We saw some damage to electronic components (including the voltage meter relay connected across the HRG resistor).  We made measurements with an RMS meter - not a scope or Dranetz.
Notes:  On one ungrounded sub once I saw 550V DC on multiple phases of a sub - it was being generated by some sort of through fault on an 480V SCR feeding an oil heater.
As busbar notes, you can build your own HRG with some transformers and a resistor.  We have built some portable units that we temporarily install on the ungrounded subs so we can use the pulser to track grounds.  If you are going to leave it on for a long time, you will need to make sure the components are rated for that duty.
We have seen a number of problems with Drives on ungrounded and HRG grounded subs - mainly with them not liking the fact that the ungrounded phases can go 480 to ground.  Some have mov's that are sized for a solidly grounded system and they blow taking the drive down.  I'm not close enough to the group that works on these  to understand why the drives are shutting down, but can ask.  Does the SMC that you have give a fault code?  Some of the drive manufacturers seem clueless about how to handle HRG subs's or ungrounded subs.  If you carefully read the application manual, they often say thet you need an isolation 480Delta/480 Wye isolation trasformer in front of the drive.
Comment on the first link in the previous posting. The MOVs can dissipate so much of energy only, e.g. 160 Joules/phase conductor as included in schematics therein. If the energy in overvoltages, e.g. transients due to arcing are more lasting, there is a good chance that the MOV will burn, if not protected by thermal sensors implementing the system shutdown and by an overvoltage relay. The high-resistance or medium resistance system grounding is a safe solution.
RJF
     The SMC units do have a fault code. We are getting "Phase Loss/Loss of Load" and sometimes "Phase Imbalance". In talking the some of the design engineers from two companies who make SMC's, isolation transformers, or reactors in front of the SMC,s will not help. One of the problems I think we are having with the model we are using, is that the faults (listed above) respond in 16 to 20 ms, and they can not be disabled. Other manufacturers build in a 10 sec  delay, plus you can disable these trips functions.
    We always use isolation transformers in front of VFD. We have two VFD with isolation transformers on these same machines. They are not dropping out. Thers is a big difference between VFD and SMC's.
    The 900 volts I referred to are tranisits. You will only see them with a fast scope or units like a Drantex.
    Because the transits are phase to ground, and not phase to phase, I almost have to beleive the "Noise" is some how getting into the microprocessor of the SMC, and it goes bonkers, and shuts down the unit. The only connection to ground the SMC's have is on the 120 volt control power to the unit.
    I agree with your statement "Some of the drive manufacturers seem clueless about how to handle HRG subs's or ungrounded subs." I did finialy get the applacation engineer at the factory to say that the model SMC I am using will not work and they did not have anything to offer to resolve the problem. It was my idea to just bypass the whold SMC and turn it off after the motor is up to speed. This is a new model, and has not been on the market very long. We may have been one of the first sites to use these in large numbers. This same manufacture a few years ago also told me I did not need isolation transsformer in fron of their VFD. From my experience Not true, with an ungrounded systems.
   There has been a lot of discussion on this forum about ungrounded 480 volt systems and the need to use HRG. I wish I could install HRG units on all of my 480 volt substations.
   Just as a finial note. We found the ground. It was an arcing ground, that was coming and going. We found it on one wire, just before it entered a motor pothead. Vibration of the equipment was causing it to  come and go. If you reed Beemer's book, this is the worst kind of ground to have. If it had beed a solid ground that stayed on, it would not have caused the problems with the SMC's and we could have found it very quickly.
   The way the electricians found this one, was by camping out in the substation. When the arcing ground returned, they quickley turned on our "Tracking Equipment" and when they did it welded the wire to ground. Now with a permenet ground they were able to track it down in about 5 min. Took another 15 to get the production department to shut down the pump, which them confermed that it was the bad guy.
  One other note. We had just installed a ground alarm system on all of our 480 volt substations. It had only been on a few weeks. I get a a notice of all grounds on the substations, on my desk computer. With out this arlarm system, we would today still not know that we had the ground we did, and it would still be there. The cost of the ground alarm system has more that paid for itself.
   Only problem now is that we are keeping two electricians busy tracing and fixing grounds. Which is good. Before the alarm system we did not know these ground existed.
   If we had HRG units, we would not have as many interminit grounds in the first place!!!
Hope this answered you questions.
…HRG units …not have as many interminit grounds…
jburn, that is a most likely a very precise assumption.  Although anecdotal, I have found a fair number of cases in the last three decades that affirmed your statement—from unbelievably frequent stator-winding insulation punchthrough on ungrounded systems. With an incredible motor “burn rate” [one facility had fourteen 480V-wye unit substations,] all but one were operated ungrounded while serving a hundreds of motors over the range of 2-500hp.  In thirteen of those particular 750-1500kVA unit subs, the XO bushings were all “flying in the breeze.”
OTOH, I have seen a number of other ungrounded plant systems with strikingly improved insulation-failure rates after high-resistance upgrades.
The grounded-wye/broken-delta transfomer arrangement is cited repeatedly in IEEE publications; applied at all voltages—although at higher voltage levels it is used for annunciation and/or protective-relaying functions, and not the sole means of directly or independently limiting transient overvoltages.
Jburn - IS the ground alarm system that you mentioned having on your subs a commercial system?  If so, who made it?  We have looked at designing our own as I have not found a commercial system.  We just use the built in alarms for HRG equipped systems.  I agree that an arcing fault can give very high and weird voltages on an ungrounded sub - an HRG is supposed to help limit voltage swings.
Made an error in my 30-Jan posting.  I referred to SMC starters as “VFDs.”  My apologies.  SMCs do not have "load-side transistors."
jburn
As a question or personal education I've always wondered about multiple failures on an ungrounded system in a large manufacturing facility.  Are you having any catastrophic failures (SCR's Motors etc...) due to the phase to ground faults?  If you are do they occur in multiples?  Do you know the source of the grounds?
RJF, and d23
    The ground alarm system is a home grown system but using all standard components. I do not have HRG on my 480 volt Delta unit subs, so I used a ground detector made by Erickson Electrical Equipment. The Erickson unit gives me a dry contact. I hooked up the Erickson to the closes, already existing, remote PLC I/O card. Because most of our PLC's are on a network, I then used a data historian system called PI, which already existed in the plant. The PI system scans the PLC remote racks, and records each time the Erickson sees a ground. The PI system time stamps each event. Using the PI system, I can look at all of the history of the grounds, and plot each event, on my desk computer. The PI system also sends me an E-Mail and a page, on each ground event. The system works quite well, as I can overlay any of the other 18,000 data points in the PI system, to look for any corralation. The system is fast enough that it picks up interminit arcing grounds.
d23,
   I have worked in several different industrial plants for 32 years. All of them had unground delta 480 volt unit subs. I have seen catastrophic failures due to the phase to ground faults, but I have never seen multiple failures, as described in Beeman's book. The problem I have just had,  shut down 5 machines at the same time. In this case there was no apperent damage. I do know the source of the grounds, and they vary. We are very agressive in tracking down each ground and fixing the problem.
    The alarm system as I decscribed above, has shown me that we are having more interminit arcing grounds than we ever knew about. Before we installed the alarm system, we had no way of knowing when we had an interminit arcing (coming and going) grounds. We were only seeing grounds that were permenit. Another benifit of the alarm system is that because we can plot the exace time all of our ground come and go, we have been able to track down the ground, with the help of operations, just knowing what equipment is cycleing on and off at the same time the grounds do. The system has well paid for itself.
Hello jburn,
I can sympothise with you as I have experienced similar problems and have only just managed to resolve them. Please advise if the starters to which you refer to are SMC3 or SMC Delta. Your location (country & state) would also be beneficial as this will assist me to identify persons able to provide localised support if need be.
Once I have the above details we can move to solve your problems.
GGOSS
GGoss
     Thanks for the offer of help. I would perfer not to name the make and/or model of the soft start controler (SMC)that we are using. I am receiving help and support from two different manufactures of SMC's, including the manufacture of the one I am using, as well as from some power quality experts, looking at system grounding, arcing ground faults, issues etc, etc.
      I would like to keep the discussion on this forum generic, dealing with power quality and solid state/ microprocesser controled equipment issues in general, on ungrounded power systems.
       The real fix to the problem has more to do with power quality, system grounding, etc, and not any one make or model of device. All of the units on the market will work fine if your systems are properly grounded, no ground loops etc, and if you address all of your power quality issues, which is where I am focusing my time.
        If you do not address grounding, and power quality issues on your power systems, from a reliability standpoint, all of the equipment on the system, like all motors, and the cables themselves are subject to failure, not just SMC's
As I understand a soft starter left online without bypassing can also perform as an energy saving device by reducing the operating voltage until a point that the required running torque is maintained. Thus the current being the same, the product is the reduced power consumption.
Selecting a bypass contactor shall be of the motor name plate rating, since the bypass is not a closed transition.
As we are aware that any electronic power device introduces harmonics into a power system, a harmonic measure of the power network at the MDB shall be done.