Fan motor with a VFD running at low frequency question
6

Fan motor with a VFD running at low frequency question

Fan motor with a VFD running at low frequency question

(OP)
Hello,

I did browse the internet a lot and only found part of the answer to a question i am asking myself.

I keep reading that running a VFD in V/Hz control mode at a low frequency will overheat the motor.
I keep reading that the magnetizing current is significant and the motor can't cool down because of its slow rotation (internal fan).

Honestly, i do not understand why the motor would overheat at a low frequency... we have a constant V/Hz ratio.
If the frequency is 0 or very low, then, the voltage will be 0 or very low.

How can a motor overheat when almost no voltage is at its terminals?
I understand that there is no cooling, but if the voltage is near 0... the current has to be near 0 too...

If a motor nominal current is 20 Amp at 600VAC/60Hz, then, at 0.5V/0.5Hz, the current should be 16mA... maybe a little more because of the magnetizing current. But the magnetizing current is constant (from the motor design) and is very small compared to the load current.

I believe there is a piece of information i am missing.

I AM NOT SEARCHING FOR A ANSWER LIKE : "WHEN YOU RUN A MOTOR AT LOW SPEED IT OVERHEATS".
I browsed google a lot and this is the only thing i found.

Does anyone have a clear explanation, a technical article or a good book reference explaining this?
Thank you very much!

RE: Fan motor with a VFD running at low frequency question

2
The constant V/Hz ratio is not really constant. And the motor voltage isn't near zero volts at low speeds.
There is always enough voltage to produce the required magnetization current. So, if you measure the voltage that actually exists across motor windings you will find something like ten or twenty percent of rated voltage also at very low speeds.
That voltage drives the magnetization current, which heats the motor.
The heat removal is not adequate when the air flow is low. So the motor overheats.
So, even if you do not like it, I have to anser that moroe overheats when running at low speed. If there is no other cooling, like external air or water cooling. Which you usually find on motors that motors that are used in paper Machines, Rolling mills and other applications where you have a high max/min speed ratio.

Be nicer when you ask questions. No need to start with flames.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Fan motor with a VFD running at low frequency question

(OP)
Lol, i was not being harsh, i was just asking to not receive the answer i can google anytime and find on any forums, but wanted a more detailed answer.

And you gave me an answer to clarifies one thing:
The V/Hz is theoritical and drive application kind of "lie" when they don't mention the details you just pointed out at me.

Thank you very much.
I will try measuring that this afternoon.

By the way, isn't the magnetizing current more around 1-2% of the nominal current?

RE: Fan motor with a VFD running at low frequency question

2
OK, I understand.

No, the magnetization current is more like 50 - 70 percent of rated current. It can be even higher That is what makes the Power Factor of asynchronuous motors so low.

Another thing that may upset you ( bigsmile ) is that you will find a voltage that is unexpectedly high. That is because the voltage is composed of pulse-width modulated voltage pulses that have a constant and high amplitude. The voltage and the currents you SHOULD measure is the fundamental frequency, the frequency that determines motor speed.

If you measure that voltage with a volt-meter (RMS or not) you will get a high reading. Use either a "1 V/Hz" filter or a system that can give you the spectrum of the voltage. Then look at the lowest peak, frequency-wise. It shows the value of the fundamental frequency.
There is a lot of problems with such a measurement, like extreme EMI being present, and that can make such a measurement impossible if you do not use an isolation amplifier with 60 to 80 dB CMR.

But, OK, go on. You will learn a lot from what you see. And slowly realize that theory is somewhat different from reality. And, in my World, reality has a tendency to be what Counts.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Fan motor with a VFD running at low frequency question

(OP)
I only have a Fluke 85V here with me.
But, I managed to read approximately:

- 20V @ 0Hz
- 60V @ 3-4Hz
- 300V @ 15Hz

So, i guess that the linear V/Hz ratio only sets in after you passed the V/Hz Mid point (probably around 10 Hz).

I have really been misguided by the fact that in reality the magnetizing current of an AC motor is high.
I always thought it would be low like a transformer after its inrush.

I guess I will set the minimum frequency at 30Hz. This way, i will be sure the motor spins quickly enough to cool itself. As a matter of facts, for our appilcation, i could set the minimum frequency at 60Hz since its the only speed i have interest in.

Thank you very much.
Coco

RE: Fan motor with a VFD running at low frequency question

A large part of the motor impedance is inductive reactance. Inductive reactance is proportional to the frequency.
As the frequency drops, it takes less voltage to force rated current through the motor.
Heating depends mostly on I2R.
R- Resistance is constant.
At slow speed, if the load demands full load current, the heating will be the almost same as at full speed, but with much less air movement to remove the heat.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Fan motor with a VFD running at low frequency question

Hi Coco,
The answer to your question is that it depends upon the nature of the load - is your load variable or constant torque?

A variable torque load can run at extremely low speeds with little or no chance of overloading (ie over-heating) the motor. Variable torque loads include centrifugal type fans & pumps.

A constant torque load cannot run at extremely low speeds without some means of external cooling. Generally most motors are capable of proving at 2:1 speed turn-down. Any greater than that an external blower motor is often recommended. Talk to your motor OEM wrt this issue. Constant torque loads include conveyors, constant-displacement pumps.

GG

"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)

RE: Fan motor with a VFD running at low frequency question

It also depends on the cooling system of the motor. TENV motors are designed to not need cooling fans, they dissipate the rotor heat (which is a bigger problem) through the shaft, so they tend to hold up better in "Inverter Duty" applications. However, you will find they are limited in size; I've never seen one larger than 30HP (22kW).

What you will find, or want to look for, with regard to cooling and speed is what's called the "turn down ratio" when using or specifying a motor for use with an inverter drive. So a ratio of 4:1 is typical for a "standard" motor. That means if designed for 60Hz, you can operate it down to 15Hz (12.5Hz if designed for 50Hz), but lower than that and it will likely over heat. TEFC "Inverter Duty" motors are often rated for 10:1 speed range and TENV motors (within the size range mentioned) or if larger, TEBC ("Blower Cooled") are often rated for 1000:1 turn-down, meaning you can operate them down to .06hz (basically zero speed).


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

RE: Fan motor with a VFD running at low frequency question

Coco Eng,
if you are using a variable speed controlled, you have to consider there are lot of harmonics generated from the VFD.
Lots of these are present either at full speed and no speed due to sinusoidal current reconstruction.
These armonics travel on iron base of the motor and rise the heat of the motor.
Furthermore some harmonics have Positive phase, some other negative phase and some other neutral.
These positive and negative phase are inline or 180° apart from foundamental Hz (50 or 60).
It is quite common in VFD find motor with high temperature at low speed because lot harmonics and no right cooling present.
These type of motors normally need a constant speed cooling fan on it..

Regards

RE: Fan motor with a VFD running at low frequency question

That was more of a concern long time ago. When GTO:s and other slow devices were used for switching and the switching pattern was very "primitive", Think Full Block switching and "Full Block with Edge Notches". The faster switches, like IGBT and others, changed that. There are very few "harmonics" in motor current and flux today. The main problem is that the low speed built-in fan doesn't remove enough heat.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Fan motor with a VFD running at low frequency question

Skogsgurra,
sincerly in my experiencies the harmonics are present on Motor and can be also found with vibration analysis (this means the electric components stressing all mechanical parts of the motor).
The devices i'm talking about are relatively recent (ABB, SIEMENS...) and they produce as default (but ti is possible to change) 2Khz as switching frequency.
Furthermore consider that these frequency normally is not alone but is carrier frequency for other modulating frequencies combining togheter running through baseplate and generate heating.
As before, the best way adopted from ABB for a slow speed motor vith VFD is to connect a steady state fan as a cooler rear to the motor.

RE: Fan motor with a VFD running at low frequency question

Sure. But it was much worse before. And it is not about harmonics in its correct sense today.

Yes, you can see the vibrations if you do vibration analysis. But those vibrations are not from torque variations, like you had when the switching was crude. They are more a result of magnetostrictive forces (that produces audible sound as well).

The ABB Direct Torque sometimes produces torque variations when switching between the "inner and outer flux circles" and the tolerance is set high to allow for lower switching frequencies. It used to be so. But I still say that this is not of any major concern when it comes to heating in modern VFD:s. The misconception is still live and kicking. Just like the thinking that you only get bearing currents in larger motors and that Insocoat bearings help. Technology Changes. And Old Truths still live on.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Fan motor with a VFD running at low frequency question

Gunnar: "Technology Changes. And Old Truths still live on. " So true.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Fan motor with a VFD running at low frequency question

I disagree wit lot of part of your sentence... but this is not right place ...

RE: Fan motor with a VFD running at low frequency question

The Total Harmonic Distortion (Ithd) is considerably higher when the motor is running at lower speeds than when at 100% load. ie. much higher currents in the 5th and 7th harmonic components creating heat.

RE: Fan motor with a VFD running at low frequency question

The THD measured where - in the motor, or in the supply?

RE: Fan motor with a VFD running at low frequency question

In the Motor supply cables

RE: Fan motor with a VFD running at low frequency question

On a type with a plain rectifier that's true, but many larger drives now have an active PFC front end to meet harmonic distortion legislation. Sure there's a little bit of switching noise but it can be filtered out reasonably easily.

RE: Fan motor with a VFD running at low frequency question

greybr. & Sofist

Do you have any waveforms, RMS for fundamental and harmonics? It would be interesting to compare with my numbers from a set of measurements I did just to see the difference between older drives and newer ones. My results do not show any excessive heating from harmonics in the motor current at low speeds.

BTW: You work at the same facility?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Fan motor with a VFD running at low frequency question

With fans, the cooling really is a non-issue. You won't be running a fan motor so slowly it won't cool or it would be pointless to even have the fan running at all.

Now bringing up another question. Why are you using a VFD if you're going to run at 60Hz all the time?

RE: Fan motor with a VFD running at low frequency question

LH, I don't believe he ever said he was going to run it at 60Hz all the time. In fact his question was ABOUT running it at low speeds.

But your other point is a good one, that with a centrifugal load like a fan, at some low speed the fan not longer moves enough air to be able to overcome static pressure so although there is almost no load on the motor making it unlikely to overload or over heat, it's also pointless to run it at all because it is serving no purpose either.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

RE: Fan motor with a VFD running at low frequency question

(OP)
Thank you all.
The discussion is very useful.

Indeed jraef, my question was more to understand what happens and what is implied when running a motor at low speed than actually using it at low speed. I wanted to understand how to properly protect the motor and what conditions were dangerous for the motor.

This whole discussion has been greatly appreciated.

RE: Fan motor with a VFD running at low frequency question

Still waiting for the data from greybr. & Sofist...

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Fan motor with a VFD running at low frequency question

Yes, running at 60Hz was posted.

8 Apr 18 16:55 - "As a matter of facts, for our appilcation, i could set the minimum frequency at 60Hz since its the only speed i have interest in."

I was just asking, why use a VFD on a constant speed application and add about 5% to the losses of the system?

RE: Fan motor with a VFD running at low frequency question

(OP)
Only because I do the commissioning of the system and it is not me who designed it nor wrote the performance requirements of the project :)

RE: Fan motor with a VFD running at low frequency question

Ah, missed that.

Coco_Eng,
If you are concerned about protection and very low speeds, it's common for people to use embedded thermistors (or RTDs) in the motor as an added feedback of actual stator temperature. Most VFDs have the ability to accept a thermistor input from the motor as one of the inputs to the drive and use that to supplement the OL protection scheme, some can also accept RTDs or have an accessory card that will accept them. In fact if the motor is rated for classified (Ex) areas, it is a requirement in may jurisdictions. The thing is though, the motor must have the thermistors (or RTDs) embedded in it already.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

RE: Fan motor with a VFD running at low frequency question

Hi Coco_Eng,
in attachnment some measuraments made on a ABB/Schnider/(other don't remember name) VFD with 2 type of filter (to motor and to line).
The measurements made on a cable to motor.
At the end you can see comparison of signal with inverter and without (but in this case there was a 3th harmonics high so i compared a VFD output respect to sinusoidal with one Harmonic).

Hoping to give you some help

Regards

RE: Fan motor with a VFD running at low frequency question

Skogsgurra asked if I had any waveforms - now attached

RE: Fan motor with a VFD running at low frequency question

graybrookie - You're showing the harmonics on the input to the VFD, not the harmonics going to the motor. The 5th and 7th input harmonic current levels rising as the load is reduced is rather odd.

RE: Fan motor with a VFD running at low frequency question

LioneHutz. The illustration shows the harmonics generated by the VFD in the creation of the PWM waveform controlling the motor speed. The increase in harmonic current as the load reduces, maybe not what you would expect, but is exactly what happens in practice. The illustration was taken from a live recording.

RE: Fan motor with a VFD running at low frequency question

Yes, Greyb. That is right - apart from not being the motor current, which the discussion is about. The reason that THDi increases with reduced load is that the peak rectification that charges the DC link capacitors takes less time (smaller conduction angle) the less current you draw from it. Shorter current pulses means more harmonics. A simple and well known fact. But, the discussion here is about motor heating and speed and that is where Sofist's recordings comes in.

Let's study the example with the lowest load. The one where fundamental voltage is 255 V:
The first comment is that it is not percentage that heats the motor - it is actual current. In amperes.
Second, there are no even harmonics in the output of a VFD. Only odd ones, like third, fifth, seventh etcetera. The recordings show lots of even harmonics - dominating, actually. The reason for this is explained below.
Third,the "plausible" harmonics (third, fifth, seventh etcetera) make up less than 5% of the total current. That means that they would contribute with less than one quarter percent of the heating. Which wouldn't worry me the least.

So, why are there so high levels of even harmonics in the analysis? The answer is that there are lots of interference from the PWM edges and that the PQ instrument (looks like a Dranetz) cannot handle those high frequencis (to low sample rate) and that it doesn't have an adequate anti-alias filter built in.

In such cases, it tries to interpret the input signal the best it can and, since the frequencies above the Nyquist frequency are fold back to the frequency range it is designed to handle - aka aliasing - it sums all the energies it can see, including the alias frequencies, and puts them in the available harmonics bins. That is how you get a lot of the non-existing even harmonics and also a fair share of extra odd harmonics.

If you do the measurements with carefully protected signal paths and an LP filter (single pole usually works very well) with f0 at around 3 kHz, you will get an antirely different result. And much closer to reality.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Fan motor with a VFD running at low frequency question

Well, considering how little it appears your waveforms change in your recordings, I don't believe they are accurate.

I just went back and looked at some recordings I made with a 3% reactor. When the load dropped from 100% to 30%, the current peaks dropped from about 100A to 55A. So, I find it very hard to believe that your readings with the the current peaks increasing when going from 100% load to 30% load on the motor are accurate. It appears the peaks in your waveforms actually increase as the load is reduced, which simply makes no sense.

Anyways, this has nothing to do with the harmonics reaching the motor and are not indicative of any extra heating effects in the motor.

RE: Fan motor with a VFD running at low frequency question

Gunner - I hadn't commented on the data from Sofistioelevib, but it did appear to be data from a typical power quality analyser, and from what I have seen I'd agree that most of them are not suitable to use on the output of a VFD and therefore can't be expected to be trustworthy.

RE: Fan motor with a VFD running at low frequency question

Yes, Lionel. It has always been like that. They are PQ instruments and not motor analyzers. Their CMRR is terrible and I usually disconnect the voltage paths and put brass foil with ground straps between Cable and current clamps. That way, you can use a Drantz - sometimes.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close