Hello Fellow Engineers,

I'm looking for an exact reference to the situation of blowing a high side fuse on a delta-wye(gnd) connected power transformer(single phasing).  From experience I know that when this occurs, the result is about a 1/3 voltage drop on the low side phase-neutral voltage...(i.e. on a 120V base, I measure about 80V when I lose a high side fuse at the sub).
I don't think the calculation is that simple.  I've tried about every source I can think of to find an example calculation for when this problem occurs.
The reason I need this info is for breaker low voltage trip settings at the substations to avoid single phasing claims on motors and such.

Thanks in advance,
Plinko

RE: Single phasing a delta-wye(gnd) TFR

Suggestion: Please, would you elaborate. The delta - wye transformers have some voltage angle between the primary and secondary voltages, e.g. 30deg leading, lagging, 90deg, etc. Also, there will be different values of voltages in the secondary wye because of voltage asymmetries.

RE: Single phasing a delta-wye(gnd) TFR


J Horak and G F Johnson—Basler Electric Company, A Practical Guide for Detecting Single-Phasing on a Three-Phase Power System, Western Protective Relay Conference, October 2002, Washington State University
  

RE: Single phasing a delta-wye(gnd) TFR

Suggestion: Visit
http://www.basler.com/downloads/practical.pdf
for the referenced paper.
However, the 80V appears to be somewhat high for the loss of one phase on the delta-wye transformer primary.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources