Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

(OP)
Hi Guys,

I' m struggling with an issue regarding bolt minimum acceptable pretension. I'm designing a clamp for aluminium tube (DN 50)and I'm using finite element analysis to check bolt loads and loads on tube. Bolts are M5 and if I follow available bolt pretension suggested by different manufacturers and charts Aluminium tube would collapse due to high pretension even if I increase thickness of tube. In this situation I want to know what minimum acceptable bolt pretension is to avoid loosing clamp and keeping clamp in its place.
Schematic shape of clamp is presented on below website:

http://www.pipingtech.com/products/ptpcat/support/...

please note "C" value should be 2mm.


Thank so much

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

That depends on how much force and/or vibration and/or torque is trying to slide the clamp along or rotate the clamp relative to the tube.

What, exactly, is the purpose of the clamp?

What is the environment (fluid, temperature, pressure, velocity) inside and outside the tube?



Mike Halloran
Pembroke Pines, FL, USA

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

Can you use a Belleville washer?

Dik

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

(OP)
Washer cannot be used. Also, the purpose of clamp is supporting of a piping system. water is inside the tubes and temperature is amb. with low pressure. no possibility to using rubber for inside of clamp.

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

If you can't pretension normally I wouldn't even consider it as being effective. Locktite it, pin it, or safety wire it and be done with it.

Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries
https://www.facebook.com/AmericanConcrete/

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

I have never messed with aluminum clamp connection before, but I know for steel pipes it is not uncommon for a pipe to experience yielding before it reaches the pretension that the bolt is capable of.

What is the nominal sliding force you have to resist and is their any nominal twisting force the clamp connection has to resist?

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

Locktite Red works really well... and I've never had anything using it ever loosen... even with the firm application of a wrench...

Check with the manufacturer to see if OK with aluminum... also aluminum has a higher coef of linear expansion.

Do you have issues with galvanic corrosion?


Dik

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

mosii,

The last time I designed a tube structure that had clamping bolts, I specified that the holes were to be drilled through plugs welded through the tube. That way, the bolts clamped on solid material and and could be tightened down hard. Your next choice is to not drill through the aluminium tube. Weld a flange on one side and drill through that.

Bolts come loose because they are not tightened down hard. You need your design to allow you tighten bolts down hard.

--
JHG

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

and if aluminium material, careful with damaging the bearing surface...

Dik

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

Quote:

(mosii)

In this situation I want to know what minimum acceptable bolt pretension is to avoid loosing clamp and keeping clamp in its place.

If you can't clamp to the yield strength of the material......then a minimum to use is 15%. That is recommended in ACI 351.3R-04 (but acknowledges that it may not be adequate for high vibration situations). That should get it "snug" tight......but that is for machinery hold-down....not sure if this would be adequate for sealing up a pipe that has water in it.

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

Unless crushing the tube is a requirement, that's a terrible clamp design.

To just hold the tube up, a simple loop of rope around the tube and some stationary object would do just fine.

If the clamp needs to resist thrust, you need to find out how much.

If the tube will be vibrating because of pressure fluctuations, you might need something like the stackable plastic clamps used on machine tools' hydraulic tubing.


Mike Halloran
Pembroke Pines, FL, USA

RE: Minimum Acceptable Bolt Pretension to Avoid Loosing Clamp

Quote (warose)

If you can't clamp to the yield strength of the material.....

The expression, "Tighten 'er till she cracks, then, back off half a turn", comes to mind.

Dik

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources