Workable gages in 3x3 angle leg
I would just like to verify that in AISC Table 1-7A, for a 3" leg angle, it shows that there is NO workable g1 & g2. Am I reading this correctly?
If I wanted to design a connection for a single angle I would need to use a minimum of 5" leg angle.
RE: Workable gages in 3x3 angle leg
For any angle leg, if you can fit them, you can use staggered bolts as long as you can provide the recommended minimum bolt hole edge distance (AISC Table J3.4) and conversely provide clearance off the orthogonal leg for nut/washer clearance and wrench access (AISC 14th Ed Tables 7-15 and 7-16).
@JAE- I am analyzing a L3x3x1/4 single angle shear connection. The bolt diameter is 5/8". My g1 value is currently 2".(see attachment http://files.engineering.com/getfile.aspx?folder=5... ) In AISC 14th edition, for single angle connection, Table 10-11 shows 3" for g1. I want to verify that I can use 2" according to AISC.
@CANPRO- I am analyzing a L3x3x1/4 single angle shear connection. The bolt diameter is 5/8".
Is this for the W8 connection? Why the need to space so tightly?
You can use a L4x3 for a single leg connection. Shop weld the 3" leg to the girder and bolt the 4" leg.