Design of boiler blowdown piping
Does boiler blowdown piping need to have sweep elbows (3 x radius) or double 45* elbows? I have some info from a boiler inspector requesting this on our blowdown piping but can not find any documentation to support this.
Thanks!
RE: Design of boiler blowdown piping
May check the AMSE B31.1 Power Piping Code for the design requirements of the Boiling blowdown piping for your system.
B31.1 Section 122.2 has a should statement for 3D pipe bends.
"...should..." and "must" are two different animals.
From 2016, B31.1 Section 100.2
should: “should” or “it is recommended” is used to indicate that a provision is not mandatory but recommended as good practice.
suggest using good engineering judgement as you likely know the overall system layout and requirements.