Rebound Hammer Test
Rebound Hammer Test
Hello everyone!
I involved in a marine foundation project where rock socketed steel H-piles were constructed (see attached).
The piles are roughly 20m deep sitting on the bedrock, each pile consisted of a permanent steel casing of 610mm dia. inside placed with a steel h-section.
Grout of 50MPa was poured by tremie method (where the grout pipe remain at the pile base from start to finish) to fill the void between the steel H section and the permanent steel casing.
Grout cubes were sampled from the 1st batch of grout mix for compressive strength test (it took 25 batch to complete 1 pile).
However, the Contractor later found that the 28 day strength of the cubes were just 45MPa.
Instead of using a rotary drilling rig to drill a full depth verification core from the pile for compressive strength test, the Contractor claimed that conducting rebound hammer test on the top surface of the pile is sufficient to verify the strength as
1. Top surface of the grout is the weakest because it was the first batch of grout poured contacting with and displacing the soil debris inside the pile base;
2. The grout is only designed to transfer loading from the steel H piles to the rock socket (casing stop at the rockhead and grout in contact with the 5m rock socket), and grout of 45MPa was checked to be sufficient in providing the bond stress;
3. Coring on the pile is difficult which may damage the H-pile if the drilling was not properly control. Also, backfilling of the core hole with new grout may cause undesirable crack as the new grout will shrink and expansion again.
Is the Contractor correct?
RE: Rebound Hammer Test
Dik
As dik mentioned, check to see if 50 MPa is really required. Somehow with a steel casing and a steel H pile I doubt the concrete is really doing much besides providing confinement for the H pile.
Dik
Dik
The method of verification for low strength samples (normally cores) should be in the specs.
Dik
But is the Contractor right about point 1 & 3?