(OP)
I am trying to design refrigeration cycle with propylene refrigerant. I am planning to use heat exchanger for subcooling of liquid and superheating of vapor. I choose centrifugal compressor and water-cooled type of condenser. Evaporating temperature is -38C. It is needed to cool down light hydrocarbons from -26C to -35C. Could you please check the datas I wrote?
In Pressure-Enthaply
A - after condenser (0.62 MPa , 5C)
A* - after subcooling HE (0.62MPa, -10C)
B - after throttling valve (0.16MPa, -38C)
C - after evaporator (0.16 MPa, -38C)
C* - after superheating HE (0.16MPa, -14C)
D - after compressor (0.62 MPa, 50C)
E - condenser (0.62 MPa, 5C)

RE: Refrigeration cycle

normally (industrial plants) evaporator and condenser have sections for supeheating and subcooling, you can estimate in/out operating points for the different units with Mollier, a table or some software (for example Prode or Refprop)... start with dP (in condenser and evaporator) < 0.5 Bar, then optimize with available data for the different units (exchangers, piping, compressor, valve)

RE: Refrigeration cycle

(OP)
I could not download Reprop, so I am trying to use Coolpack software. Is dP is pressure drop across evaporator or condenser?

RE: Refrigeration cycle

of course there are free versions but the prices for commercial versions of Refprop, Prode Properties etc. are in the 200 .. 300 dollars range... if you get some money from your work that is not a large expense...
yes, you can adopt 0.5 bar dP as initial guess for condenser and evaporator, then you can optimize...

RE: Refrigeration cycle

Isn't it of those chemicals that's ban from being used as a refrigerant by virtue of its flammable property?

RE: Refrigeration cycle

yes, all refrigerants identified as flammability Class 3 in ANSI / ASHRAE Standard 34 – 2013

RE: Refrigeration cycle

The condensor temp of 5degC is unusually low for a water cooled HX - typically it would be 40-45degC, depending on the cooling water supply temp at this location, which could go as high as 30degC in summer in many locations. Agreed, you should account for the dp across each HX also.
You should also look at the recycle case for this compressor to see how process parameters change, and that refrigeration capability is still maintained over the entire recycle flow range ( 0-100% recycle) - this will tell you what additional equipment is required / and how the recycle is to be enabled.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources