Can I get the NEC code that requires I supply splash proof Bus Duct in a Trash Area: Bus Duct is 12' above AFF.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Bus Duct
I'd be very careful with bus duct in a wet (or even a 'damp' area). I would strongly recommend that you consider cable bus. I have not spec'd bus duct in more than 30 years, it's cable-bus all the way.
BTW what are the voltage and ampacity requirements? Approximate length?
ps I am not aware of any Code that defines the enclosure rating for bus-duct in a trash area. Is this actually a wet or damp area? Is it indoors or outdoors? What has the mounting elevation of 12ft above FF have to do with the enclosure rating?
GG
"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)
RE: Bus Duct
I do not know much about bus ducts but a co-worker some time ago passed me this catalog (attached) that he was using to select an outside bus duct system.
Maybe it can help you a little.
Good luck!
JBC
.......
"The more I read, the more I acquire, the more certain I am that I know nothing"