SLOPING BEAM FORCES AND MOMENTS FORMULAE
Hi All,
Simple question - roof beam sloping and I just want to double check that I'm calculating the shear, moment and axial loads in the member correctly. See attached for formulae that I am arriving at.
Obviously, let's say the snow and the dead load of the member will act vertically so the UDL on the beam will be wCos(a), with (a) being the angle of the beam. Thus, the axial component of this will be wSin(a), then times the length of the beam, correct?
Also, if this becomes a two span beam, I'd imagine the axial force formula wouldn't change, just the moment and shear formulae?
Is this the correct way of analysing this?
Thanks so much, working myself into a tizzy over this, needlessly no doubt!
RE: SLOPING BEAM FORCES AND MOMENTS FORMULAE
or you can project the load into the beam axes, which would reduce the normal load, by cos(slope_angle), and give the beam an axial load component.
humm ...
EDIT: WTL1 above should be multiplied by H/R for the purposes of moment calculation.
BA
Thanks so much for your inputs.
WARose - I think WTL1 should be drawn perpendicular in your first sketch above, if R is the length being taken, right?
For Member self weight, I agree.
For finishes (e.g. roof tiles/slates and loads are on the global axis), I still need to multiple this my Cos(a) to get the load perpendicular to the beam - just like snow, correct?
rb1957 - What is the axial component if I multiply the snow and dead loads by Cos(a) to obtain a UDL perpendiculat to the beam, and taking the hyprothenuse as the length of the beam?
Thanks guys!
H/L = cosθ.
Therefore, load normal to beam's local axis would be W * (cosθ)2
And Moment would be W * (cosθ)2 * L2 / 8
W * H2/8 = W * (cosθ)2 * L2/8
H = L cosθ
Another good resource.
http://www.learnaboutstructures.com/Determinate-Fr...
Correct. Perpendicular to the span (at least for the purposes of moment calculation). That means WTL1 should be multiplied by H/R.
Good catch.....I will update my post above to note that.
If you have Bryer's book on wood design.....he goes through this. (I think very effectively.)
it looks to me as though wt1 normal to the surface (maybe a component of a down load) and so moment would be xR
and wt2 is the vertical component and moment would be xH (the horizontal component of the sloping roof).
cos^2 looks odd to me ... I can see cos as either the projected length or the projected load, but not cos^2 ??
WTL1 is part of the "sloping beam method"; WTL2 is part of the "horizontal plane method". (The latter being more popular in wood design.) WTL1 is drawn correctly, but I forgot to note you need to take components to plug into the moment equation. Also, calculating the shear (i.e. wl/2) with WTL2 will give you a conservative result (higher than the actual value).
The moment is W*R*cosθ/8 where W is the total gravity load on the beam and R is the sloping length of the beam. This is the same as W*H/8 where H is the horizontal span.
BA
If we define lower case 'w' to represent UDL per unit length of horizontal projection and upper case 'W' to represent total gravity load on the beam, then:
1. M = wH2/8
2. M = w(Lcosθ)2/8
3. M = WH/8
4. M = WLcosθ/8
are all equivalent expressions for moment
BA
https://www.aisc.org/globalassets/modern-steel/arc...
I think joist mfrs assume the axial component is resisted by the diaphragm even though the joist is stable without this assumption since there would still just be a vertical reaction at each end of the joist without the diaphragm assumption. They would then not design the joist for the axial component. A lot of engineers probably also assume this with beams and diaphragms. I don't 100% agree with this.