HAP report cooling load difference
HAP report cooling load difference
(OP)
I got a HAP file from a designer. The Total Sensible Coil Load is 200 MBH. However, in the table below which shows space-wise sensible cooling loads sums up to be around 49 MBH. I am unable to comprehend why this difference? HAP file is attached herewith.





RE: HAP report cooling load difference
It seems that this design has a large proportion of outdoor air (~84%). This is going to be a large contribution to your coil load.
Whether the inputs to this calculation are correct is another question, the OA percentage seems very high.
RE: HAP report cooling load difference
RE: HAP report cooling load difference