Dual rated CT

Dual rated CT

Dual rated CT

(OP)
Dear friends
Does anybody knows about dual rated CT's
Is it single core suitable for metering and protection?
Or two core CT (1 metering and 1 protection) is called as dual rated CT

Thanks

RE: Dual rated CT

In the US, a dual-rated CT is one that has a protection class and a metering class, and should be tested to verify both at the factory.
A "two-core" is referred to as a dual-core CT which is two separate cores contained in one housing.

RE: Dual rated CT

Every protection CT is a dual rated CT.
For example, a 5P CT is supposed to meet Class-1 accuracy requirement in the load current range.
The problem arises when the client stipulates Instrument Security Factor (Fs) for metering requirement. Protection class CT will not meet this requirement.

Rompicherla Raghunath

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources