Remember, we are talking about names given to the solution to formulas.
All that is happening is that the current waveform is displaced from the voltage waveform. (The cosine of the angle of displacement is called the "Power Factor".
Exporting reactive power?
This is adjusting or correcting the phase angle of the offset between the voltage waveform and the current waveform.
Power Factor
The cosine of the angle by which the voltage and the current waveform differ.
Exporting VARs is changing the angle between the voltage and the current, most often in a favourable direction.
Importing VARs is changing the angle between the voltage and the current, most often in an unfavourable direction.
The capacity of a transmission line is often limited by the amount of voltage drop that the online tap changers can correct.
On a long transmission line, a large part of the voltage drop may be reactive, caused by the inductive reactance of the line itself.
In effect, the transmission line is a series reactance.
If this voltage drop can be compensated, the capacity of the transmission line may be increased.
This may be done at the receiving end, or by several installations distributed along the line.
The correction may be done by capacitors, synchronous condensers, or by over over-excited generators.
Also, a poor power factor load will cause excess reactive voltage drop on the transmission line.
I have seen capacitors used in two series capacitor stations spaced along a long 500 kV transmission line.
I have seen a large mine mill that used large synchronous condensers to correct the power factor of the mill, with the possibility of over-correcting the power factor of the mill to reduce the voltage drop of the transmission line feeding the mill.
Note: Over-correcting will affect the power factor penalties and would only be done with the consent of the supply authority.
The most interesting correction was a large city fed by a long transmission line. The city was originally supplied by diesel generators. When the transmission line was built, the generation plant was mothballed.
Many years later, the growing city reached the limit of the capacity of the transmission line due to voltage drop issues.
The diesel plant was re-commissioned and put online.
The generators produced very little real power. This is controlled by the throttle position of the prime movers. The generators were over-excited to compensate for part of the transmission line voltage drop. An added advantage to correcting the phase angle of the transmission was a reduced transmission line current and the associated reduction in transmission line losses.
It would not be unusual for the voltage at the load end of the line to be higher than the voltage at the supply end of the line.
Bill
--------------------