Hi all.
There is ABB Sace Emax 2.2N circuit breaker with Ekip dip LI electronic protection unit. It contains a terminal for connection of control voltage to shunt trip coil via NO contact controlled by protection unit. Since protection unit must cause CB to be opened in the case of fault regardlessly of trip coil presence (installed or not), what is the purpose of this control circuit? Is it just additional safety measure for fault current interruption, or some other utilisation of this feature is foreseen?

RE: Shunt trip coil controlled by electronic protection unit


MikiBg,
We use the shunt trip breakers for equipment interlock or to have remote breaker open capability.
-JFPE

RE: Shunt trip coil controlled by electronic protection unit

(OP)
Yes, that's why I am asking. In this way CB will not be controlled remotelly, but locally by protection unit providing control voltage to shunt trip coil.

RE: Shunt trip coil controlled by electronic protection unit

If there's no trip coil, the external relay won't do anything. The internal trip unit will always trip the breaker.

RE: Shunt trip coil controlled by electronic protection unit

I think what you are seeing is that your breaker has an ETU that acts on a shunt trip internally, and they give you access to that shunt trip if you want to use it for something else.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

RE: Shunt trip coil controlled by electronic protection unit

(OP)
Mystery solved by browsing other files. A terminal I was referring to serves for connection of control voltage to additional (optional) module which can be controlled remotely by communication interface. This module acts on shunt trip coil. Of course, there is another terminal for traditional, hardwired excitation of trip coil directly.
Confusion has been mainly done by catalog explaining function of questionable circuit as "opening coil with control from protection trip unit". Poor and confusing documentation given by ABB in my opinion.
Thank you all for participation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources