In-rack arrangement - Single or double row racks?
I am looking for the correct sprinkler arrangement in protecting single row racks over 7.6 m (25') height for class I through IV per NFPA 13. The two racks form an aisle of 2.7 m (8'-10"). The outside faces of the racks are free to open space from one side and 1 m (3'-3") away from a wall from the other side. The racks have a width of 2.3 m (7'-6") each with no longitudinal space in them.
According to the definition of NFPA 13, par. 3.9.3.7.7 a single rack can have a width up to 6 ft (1.8 m) to fall in this category. My understanding, therefore, is the racks I have need to be classified as double row racks and follow double row in-rack sprinkler arrangement. However there is no longitudinal flue space to place the sprinklers. So, does this mean that the sprinklers need to be placed as face sprinklers? If this is really so, the sprinklers will not be able to cover the commodity entirely as they will be more than 6 ft (1.8 m) away from the far side of the rack face. Would that be acceptable or a middle row arrangement in the rack, typical for single racks, is more appropriate/acceptable?
Thank you.
Thank you.
RE: In-rack arrangement - Single or double row racks?