thread237-127598 hello every o
thread237-127598: Y Start / Delta Run, but 'normal' Motor Y Run?
hello every one.
i have motor 30 kw , 3 phase,9 leads,with installed 440 volt, 60 hz. actually the 9 leads terminal is connected as follow :
1 , 2 ,3 , 4&7,5&8, 6&9. this is sex terminal.
my question is : how i can connected it for soft starting???
choice no 1 : connect three phase 440 v to the terminal 1,2,3.
choice no 2 : as the big motor need star delta starting, how i can connect wye-delta connection to the terminal of the motor ?????
what is the correct choice 1 or 2.
please advise me.
RE: thread237-127598 hello every o
A nine lead delta motor has three internal connections that are not accessible. Six lead motors may be connected in star or delta, but 9 lead motors can not be.
You need to buy a soft starter or a Variable Frequency Drive.
If this is an easy starting load you may use a soft starter.
If this is a hard staring load that needs full torque you may need a VFD.
Your motor may be star or delta. The connections for both at the higher voltage are the same.
It doesn't matter if the motor is star or delta.
Bill
"Why not the best?"
Jimmy Carter