How to do crack control according to ACI code

How to do crack control according to ACI code

How to do crack control according to ACI code

(OP)
Hi all,

This is new engineer design with ACI code.
I am doing a pond design and want to do the crack control.

I see that ACI 350.1 10.6.4.2 has some equations for crack control.
Also I see there's one exception that while the cover is greater than 2 in. mentioned in R10.6.5.
But there's no further how-to-to in ACI 350.1 nor in ACI 318-02.

Currently I am using a cover that is greater than 2 in. so I would like to know which equations I can use for crack control.

Thanks a lot!

RE: How to do crack control according to ACI code

you may want to look at pca design guide for tank that would have a step by step how to design tank with water.
as far as i know, crack control is just a formula that will have more reinforcement and tighter spacing.

RE: How to do crack control according to ACI code

(OP)
I would have explained more correctly.

There's formulas to calculate the reinforcement and spacing, but only for structure where the cover is less than 2 in.
Since I am using cover greater than 2 in., I try to find corresponding formulas but I couldn't.

RE: How to do crack control according to ACI code

Not sure why you said the formula is only for 2" cover or less.
first off, I don't see any R10.6.5 (not used).
I see this on R10.6.4

"The numerical limitations of z = 115 and 95 kips per in. for
normal environmental exposure and severe environmental
exposure respectively correspond to limiting crack widths
of 0.010 and 0.009 in. These z values were established for
cover equal to or less than 2 in. and should be based on this
value even when cover exceeds 2 in. Additional cover may
be regarded as added protection."

it looks more to me the limitation is for 2" cover or less.
don't see anywhere the 10-5 formula is only for 2" cover or less.

RE: How to do crack control according to ACI code

the pdf didn't have R10.6.5

my copy is aci350-01

RE: How to do crack control according to ACI code

My interpretation, R10.6.5 is for "appearance" criteria only which is something you should not consider.
If you have 2001 version there is no R10.6.5 at all.

RE: How to do crack control according to ACI code

Neglect any additional cover beyond 2 inches when calculating the crack control parameter Z. Otherwise the spacing requirements become too onerous.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources