Concrete Cone Faliuer
Dear all
I face problem in calculating some parameters for anchors in base plate located on existing cross beam and no any concrete else except the concrete beam. how can i calculate parameters as Ac,N and Ac0,N by(ETA) , Kindly advise you can find the baseplate in the attached file. Thanks all
Best regards
Mohamed Maher
RE: Concrete Cone Faliuer
I'd start by assuming that all you've got for concrete is a 300 x 300 base section. Then you should be able to use a simplified hand calc or software such as Hilti Profis. If capacity is insufficient, you might consider rotating your base plate 45 degrees to create a more favorable condition for the anchors.
Your assumption is correct I have base plate 300 x 300 and rested on two crossed concrete beams which are extended as per previous
attached file , and i tried to use hilti but problem that i can't achieve inclined edge distance which is 64 mm as per attached.
as a result consultant refuse the solution and needs manual calculation which is complicated for some parameters as ACN AND A0CN.. Can you please advice regarding these parameters
My recommendation was not that you have a 300 x 300 base plate but, rather, that you should consider it a 300 x 300 pedestal. That would be conservative and keeps things simple. If you want to do a fancier analysis, it's just going to be a painful thing, no doubt about it. You'd consider the code defined failure frustum at 1:1.5 and lop off the sides where you have no material.
If I make it as Pedestal it will be very unsafe so it looks that i have to make it manual :(