Steel or Concrete Moment Frames for Slender, Single-Bay Building
I'm trying to determine the best type of lateral system for a 9 story apartment building only 17' wide x 60' long. Using a series of closely spaced steel moment frames (R=3) with a couple lines of braced frames seems to work well if I use cmu side walls and hefty concrete elements at the foundations to hold the frames down, or even deep foundations with tensile capacity which may end up being required after the geotech info comes in.
As an alternative which, the architect wants me to consider in order to minimize the floor to floor, I'm starting to look into using ordinary concrete moment frames and concrete shear walls at the core. Before I get too far into this, I'm wondering if anyone has insight into the feasibility of either system for such a relatively slender, single bay in the narrow direction, building with an aspect ratio of about 4.7? I suspect a flat plate will not work and drop beams will be needed between the columns which would end up providing a similar floor to floor as the steel system.
Does anything stand out as pointing clearly to either steel or concrete?
RE: Steel or Concrete Moment Frames for Slender, Single-Bay Building
I read that the Equivalent Frame Method is not to be used for Lateral analysis. If this is so, then what technique should be used? Can you run a portal frame by hand assuming an effective equivalent width of slab to resist lateral combined with reduced stiffness of the slab? If anyone can point me to a good text on analysis methods and modeling techniques for flat plates with lateral loads I would be grateful.
I have a STAAD 3d model running with just columns and plates and the drifts seem reasonable but the dead and live load moments from the slab are not transferring into the columns. I'm going to try to create a stiff zone at the column slab intersection using a master node at the column axis with slave nodes at the column faces and see if that works.
I would like to do the analysis using at least two methods and compare results.
1) If you're in a high seismic environment, this lateral system is usually discouraged and sometimes prohibited. End disclaimer.
2) I have experience doing the flat plate moment frame exactly once. It ended up being a bit clumsy in that you wind up with significant bottom steel at your columns all over the place. Kinda kills off the sexy regularity of the system. On the one project, we designed the building to not have concrete shafts. The owner wound up putting them in anyhow just for the feel good factor. It didn't feel to good to me because I felt that invalidated much of my analysis.
3) I'm the proud owner of a single article on this topic as shown below. That's taking you way back to 1979. I feel that you can use pretty much any analysis tool you like so long as it can be shown to be somewhat rational and accepted. I'd probably be looking at ETABS etc for at least as one of the two methods being considered for validation. I think that the key from an analysis perspective is to capture the whole "moment leakage at the joint" concept as the equivalent frame method and FEM both do.
4) As a matter of pure serendipity, I've been perusing an interesting article dealing with slab-column moment connections: http://imcyc.com/biblioteca/ArchivosPDF/Conexiones.... Perhaps you will find it interesting as well. They authors purport to have a lock on a method more rational and more predictive than the classic code version.
You mean like the ones in the Twin Towers that consisted of 2 sheets of 16mm plasterboard!
I just discussed the project yesterday with the architect and he's agreeing to go with steel for this job. I told him it would be quicker designing it in steel and that seemed to change his mind. I'm relieved, however, still glad I've done all the preliminary concrete design just to get more familiar with flat plate frames.
KootK:
ACI 318 14 Section 6.6.3 Talks about using 0.25Ig for analysis of flat plates which includes a stiffness reduction factor. However, in ACI-4213R-15, which is a guide to design of two way slab systems, section 7.2 says to use the equivalent beam width model, which results in much smaller section properties. I see no clear direction as to when the different section properties apply. In ETABS, it appears to use 0.25Ig for analysis under wind and seismic loads. Using that coupled with a narrow elev core, I was getting a passable design but would have resulted in huge uplift on the foundation.
This is the northeast, low seismic area so It appears the moment system is allowed, I'm pretty sure I will be in SDC B. Thank you for the articles, still trying to find time to read them.
Rapt & Hokie66: The stairs and elevator are at the center of the building. Now that we're going with steel I'll probably add braced frames at the stair/elev. core to help out the steel moment frames. Hopefully the uplift will be manageable.