Hipot or Megger for 50 kW motor

Hipot or Megger for 50 kW motor

Hipot or Megger for 50 kW motor

(OP)
I have been told that for lager motors a Megger test is better than a Hipot test. That is to say, lager motors will fail a Hipot test and not a Megger test (I'm not sure exactly how that makes the Megger test better). I have looked through the posts and could not find anything referencing this.

Clyde Hancock
Design & analysis of electric motors and generators
www.motorconsultants.com

RE: Hipot or Megger for 50 kW motor

A 480 Volt rated motor will be meggered at 1000 Volts DC.
The same motor will be Hi-Potted at 1960 Volts AC with a peak voltage of 2772 Volts.
The old standard was twice the working voltage plus 1000 Volts. (480V x 2) + 1000V = 1960 Volts.
Meggering is pretty standard at lower voltages (Up to 600 Volts.)
Hi-Potting is not much used anymore.
At higher voltages other more sophisticated tests are generally used.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Hipot or Megger for 50 kW motor

Megger test is not destructive insulation test method but with Hipot test motor should fail .If it is used on an essential motor and without meger test before it may be possible to make a serious technical error .
Good luck

RE: Hipot or Megger for 50 kW motor

I would look at the example of a 480v VFD rated voltage peak for 1300vpk to 1600vpk nema rated motors. As you can tell just from a spec on the motor its below the HIPOT voltage. I dont think HIPOT is a peak voltage either?

RE: Hipot or Megger for 50 kW motor

Forget the Hi-Pot. Megger the motor at 1000 VDC.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Hipot or Megger for 50 kW motor

(OP)
Thanks to all for your replies.

Clyde Hancock
Design & analysis of electric motors and generators
www.motorconsultants.com

RE: Hipot or Megger for 50 kW motor

A megger test indicates the insulation dryness and cleanliness. It does not measure the dielectric strength of the insulation. Only a Hipot will do it.

For mass produced 50 KW motors, one minute Hipot is only a type test. Some OEM's will do a quick flash HV test (which is a quick and dirty method) for all such motors.

Muthu
www.edison.co.in

RE: Hipot or Megger for 50 kW motor

(OP)
Thanks Muthu

Clyde Hancock
Design & analysis of electric motors and generators
www.motorconsultants.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close