We have provided a bridge beam over a 150mm dia surface water pipe as shown in the attached drawing.

It is buried approx. 2.28m below ground level.

The concrete sill (0.9m wide x 0.8m deep) in the attached drawing is designed to a bearing pressure of 50kN/m2

We have been asked if there is a need to bridge over this pipe at all based on the depth it is located at.

How do we go about proving that our loads are within acceptable limits for the pipe?

RE: We have provided a bridge beam over

Your terminology is difficult to understand.

What is a surface water pipe? Is that just a buried water main?

What is the purpose of the bridge beam? What is the project for? What is the piping material and strength? Are the posts temporary?

Please add some details so that it possible to understand what the project consists of.

RE: We have provided a bridge beam over

I guess your pipe is plastic material : Google "PVC buried pipe design"

RE: We have provided a bridge beam over

The best thing is to ask the pipe owner. They tend to know more about it, than any one else but I have to say from the information supplied this is a massive overreaction. Buried pipes can withstand surface loading very well and at that depth most of the load is from soil above the pipe.

They're is a lot of information on this site if you search for surface loads or pipeline crossing design.

At the worst all you need to do is add a concrete pad above the pipe but 50KPa is nothing for a6 inch pipe. Settlement under the pipe is the only big issue to consider. IMHO.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close