Field Investigation for a Wind Turbine
For a wind turbine with about 150m length, and a planned foundation B x L = 20m x 20m, is a drilling depth of 40m enough? I looked into field investigation notes online but didn't find a specific one for such a structure. Any engineer that has experience with such field investigation?
RE: Field Investigation for a Wind Turbine
Eurocode 7 requires investigations to extend to 5m beyond the base of the pile. 35m deep pile for a 150m high turbine sounds ok to me? Again its hard to know. What are your loads, expected geology etc?
www.SlideRuleEra.net
www.VacuumTubeEra.net
Having worked on a number of wind farm projects with base sizes of the order you suggest I would note that the depth of investigation required is highly dependant upon the ground conditions and whether there are any perceived underground risks e.g. cavities due to mining or highly erodible rock masses.
On the assumption that such cavities are not expected and the risk is therefore sufficiently low:
I would suggest that boreholes are specified to depths of up to approximately 40m as you suggest (2xDiameter) this should be sufficient to determine the required settlements and stiffness's with confidence. Where rockhead is encountered before this depth, such a depth would not be required - our current practice is to terminate boreholes after 5m of continuous rock coring, if prior to the specified termination depth - at this point it is reasonable to assume that rock is continuous beneath this (i.e. not a boulder).
Should no rock (or deep) be encountered within the borings, it may be that some boreholes could be terminated at shallower depths, with deeper strata properties inferred from nearby locations in order to reduce the GI costs.
Hope this helps,
J
As a geologist first and geotechnical engineer second, I just want to say, we are building these things in real places in the real world. Geology is essential to answering such questions. Is it in an area of prior glaciers? Is it underlain by limestone? Is it in the Coastal Plain? Are prominent structures typically placed on piles? Is it in the Piedmont?
I mean, how should the internet answer such OP?
2B or 10% is quite consistent with general practice; however. . .
f-d
ípapß gordo ainÆt no madre flaca!