Parking Lot Entrance Gate Bollard Foundation
Parking Lot Entrance Gate Bollard Foundation
(OP)
Does anyone have an expression, or a procedure, document, or a spreadsheet for determining the depth and diameter for entrance gate pole foundation? I am treating the foundation like a bollard.
Any suggestions/comments are appreciated.
Any suggestions/comments are appreciated.






RE: Parking Lot Entrance Gate Bollard Foundation
or....
They are fully functional impact resistant bollard systems designed (well not really) to resist a particular mass traveling at a particular speed.
The first is whatever you want to do relative to foundations - a small diameter concrete pier x 4 ft. deep with the pipe bollard set into it.
The second is a fabricated and field tested product. There aren't many calculation procedures, if any, to get you a "design".
For an entrance gate - with a pier taking lateral loads, there's this old nomograph (see also pdf attached):
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: Parking Lot Entrance Gate Bollard Foundation
Anyway - the chapter 18 IBC equations are my go to for pole embedment. (1807.3.2.1 in 2012 IBC) It is iterative.
This online calculator appears to match my spreadsheet. Although it does not limit 'd' to 12' as described in that code section.
https://www.engineersedge.com/calculators/flagpole...
RE: Parking Lot Entrance Gate Bollard Foundation
For low-speed (say 25 MPH, or less) autos, pickups, small forklifts, etc. we found that nominal 4" diameter, schedule 40 steel pipe, filled with concrete was a good compromise. For low-speed off-road trucks, bulldozers, large front end loaders, etc., 6" diameter was better.
Details of embeddment depend on the soil. We typically had poor soil, so would embed the 4" pipe about 4', the 6" pipe about 5'. The pipe was encased in a concrete cylinder with a diameter 3 times the pipe diameter (12" diameter for 4" pipe... 18" diameter for 6" pipe). For a few feet in all directions, the bollard is surrounded only by soil - to make sure the bollard "uproots" cleanly.
The 6" diameter bollards worked well... when hit by the intended heavy equipment. The 4" bollards, perhaps a little too "strong". I would cut down 4" pipe embedment a little.