I appreciate your concern, Keith. The situation may not be quite as bad as you fear. The Under Frequency Roll Off feature of the AVR will give you some protection. The UFRO drops the voltage proportionally to a frequency drop to relieve some of the load on motors and give the generator a chance to recover. While UFRO is great for overcoming motor starting dips, in your place I would probably also be looking at some type of load shedding.
Here is relay that you may like. I've never used one, I'm just going by the spec sheet.
Link
Here is the parent site:
Link
You could also use a tach on the engine.
Alternate solutions:
Voltage, when the frequency drops below 57 Hz the AVR will start to drop the voltage. Cheaper but not as dependable nor as precise as a frequency based solution.
Current: Monitoring the current would be more precise and more dependable than a voltage indication, but still not as good as frequency based protection. As it is kW and not KVA that drags the frequency down there may be PF issues.
Tried and found wanting, stay with a frequency or RPM based solution.
PC or PLC; If you have a PLC dedicated to the system you could use a simple one-shot circuit to input cycle pulses from the 60 Hz and count the number of pulses in a second.
If there is a PLC, consider using it. Myself, I would not add a PLC just for frequency monitoring, unless I was going to use it to control some timing and some fancy load shedding.
Is there any choice in fuel supply? You want the heaviest fuel available.
Up here in the winter, summer diesel fuel may gell in extreme cold, shutting down vehicles. Winter diesel fuel is about 10% lower specific gravity. That translates to about a 10% loss in power. It sounds as if you can't stand any power loss at all. It's good to be aware of the effect of a lower specific gravity fuel even if you can't do anything about it.
Keep us posted on your final solution.