Based upon the voltage, phase, and frequency indicated in the data sheet, I am assuming that you're based in the United States.
Nearly all HVAC equipment manufacturers will provide the minimum circuit ampacity (MCA) for a given piece of equipment. Since the NEC requires that the MCA be calculated at 125% of the full-load current, you can easily retrieve the full-load current (And, subsequently, the apparent power) by multiplying the MCA by 80%. Usually, the maximum overcurrent protective device (MOCPD) rating is also provided alongside with the MCA. I would not recommend referencing the kW value indicated within the data sheet. It's shown as "required capacity", which is kind of nonsensical in this context. Besides, even if you did know the input kW, there would be no way to determine the apparent power (kVA) without knowing power factor.
I'm really surprised that neither the MCA nor the MOCPD are given.