Stair Slot Length (Inelastic vs elastic drift)

Stair Slot Length (Inelastic vs elastic drift)

Stair Slot Length (Inelastic vs elastic drift)

(OP)
What do you guys typically dimension your slot connections to accomodate: inelastic or elastic? Why?

RE: Stair Slot Length (Inelastic vs elastic drift)

ASCE requires that deformation compatibility be checked using the inelastic story drift (Section 12.12.5) since that is the expected movement of the structure during an earthquake. When detailing the connection, consider the impact of underestimating the drift. If failure of the connection would cause collapse or loss of vertical load carrying capacity, consider detailing for an increased level of drift. See Section 12.12.4 for some ideas on what that might entail.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources