Combined Instrument Transformer Failure on 1 Phase
Combined Instrument Transformer Failure on 1 Phase
(OP)
Hello All, One of our high voltage combined instrument transformers has failed and has to be replaced. I am trying to figure out a way where the secondaries of the remaining two CIT's could be used to create voltage and current for the missing unit for a balanced 3 phase power system.
Will greatly appreciate the help on this matter.
Will greatly appreciate the help on this matter.






RE: Combined Instrument Transformer Failure on 1 Phase
RE: Combined Instrument Transformer Failure on 1 Phase
Thanks,
Vijay
RE: Combined Instrument Transformer Failure on 1 Phase
The unit needs to be replaced. There is no other real solution.
RE: Combined Instrument Transformer Failure on 1 Phase
ConEd did that when a plant under construction had the same problem. Load was balanced and light ( < 10% of CT) so the error wasn't large. Both parties agreed to the temporary fix for a couple months.
Some protective relaying won't work without the third phase. You can approximate the missing current by Ia + Ib = -Ic for a balanced load, but as mentioned above, no ground fault protection.
RE: Combined Instrument Transformer Failure on 1 Phase
I used metering on one line to neutral as a check on a three phase metering scheme that I was using for the first time and was unsure of. There was a close enough correlation between the single phase metering x 3 and the three phase metering to reassure me that the three phase metering was correct.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Combined Instrument Transformer Failure on 1 Phase
RE: Combined Instrument Transformer Failure on 1 Phase
RE: Combined Instrument Transformer Failure on 1 Phase
Voltage is measured across L1-L2 and L2-L3. The scheme meters on the assumption that the voltage is equal on all three phases.
The accuracy is as good as the voltage balance. If the voltages are balanced, the metering accuracy of unbalanced current is good.
The A phase CT sees the A phase component of C phase and meters the C phase component assuming that the C phase voltage is equal to A Phase voltage.
Likewise B phase CT sees the C phase component of C phase and meters the C phase component assuming that the C phase voltage is equal to B Phase voltage.
We used two element metering for years until we lost one phase of a three conductor submarine cable. A single conductor was laid parallel to the three conductor cable to replace the bad phase. It was about three feet away. This caused a reactive voltage drop on one phase. The unbalance was enough that we could no longer meter accurately with two element meters. We switched our three phase metering to three element meters.
Your question is:
"What is the percentage voltage unbalance and can you accept a similar percentage metering error?"
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Combined Instrument Transformer Failure on 1 Phase
You may be able to drop a bushing CT over a transformer bushing to meter the third phase current.
I can post the connection diagram if you need it. (The first time that I used this connection was the time that I used the single phase check meter.)
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Combined Instrument Transformer Failure on 1 Phase
Here's the connection I was thinking of, but unfortunately during the actual test it appears that A and B phase are 180 out. Can anyone explain with the math why?
RE: Combined Instrument Transformer Failure on 1 Phase
I the CT part of the metering transformer is still functional, or if you can get a large enough window transformer to drop over a bushing here is a circuit that will work.
I have used this connection a number of times.
The accuracy is as good as the voltage balance.
If the PTs are connected to A phase and C phase, then the B phase CT forces the current through both A phase and C phase current elements.
The A phase element meters the A phase component of B phase and the C phase element meters the C phase component of B phase.
This will meter unbalanced currents to the accuracy of the voltage balance.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Combined Instrument Transformer Failure on 1 Phase
We don't have spare CT available, nor do we plan on changing any phase to ground connections to phase to phase. Do you know why I am getting A and B phases to be 180 out?
RE: Combined Instrument Transformer Failure on 1 Phase
RE: Combined Instrument Transformer Failure on 1 Phase
The lack of a voltage for the third element is a problem.
You are familiar with the open delta connection to derive a third phase from two phases and a neutral.
There is a connection called a Winnipeg connection that will develop a third phase for a wye system.
The Winnipeg connection was used for distribution systems.
For metering you could use two small lighting transformers.
I would use 240:480/120:240 volt transformers wired for 240 Primary and 240 volt secondaries.
You will be applying 120 Volts to the 240 Volt windings.
Connect one transformer in parallel with the secondary of each PT.
Connect the secondaries in open delta. The voltage developed across the open delta will be the correct angle to replace the missing phase.
I suggest checking the primary and secondary voltages with a good meter to determine if there is a turns ratio error.
What type of loads do you have?
For most plants that I have seen, the phase current balance is good enough to use a 3/2 ratio.
If you have a lot of single phase loads that tend to be unbalanced, this may be better than nothing.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Combined Instrument Transformer Failure on 1 Phase
Please refer page 7-26 to 28 of MULTILIN369 relay manual for 2 CT connection.
RE: Combined Instrument Transformer Failure on 1 Phase
If it's a three wire system, all you need is two. The un-metered phase amperage will be the phasor sum of the two metered phases.
RE: Combined Instrument Transformer Failure on 1 Phase
Regards.
RE: Combined Instrument Transformer Failure on 1 Phase
Since the sum two currents (Ia + Ib) is equal to -Ic and -Ic enters the phase C current coil in the opposite direction, the meter will see an Ic current at the correct phasor position.
If your meter has the capability to display the current phasors, it would probably be showing the correct current phasor sequence.