The cables run in ladder indoors, on passing to outdoors it runs above ground in conduit. When it runs indoors, there are other cables (9 cables) laid in a single layer along with it, on passing to outdoors it runs alone. It runs in same length in both indoors and outdoors.
How do you select the derating factor for this situation? I could not find any derating factor in IEC standard for this situation?
How do you select the derating factor for this situation? I could not find any derating factor in IEC standard for this situation?
RE: Correction factor for cable laying
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Correction factor for cable laying
Following all other standard, since the protection device ratings is connected with maximum current carrying capacity[ampacity] in the actual conditions then it is clear one has to comply with the NEC recommendations in any way.So the lowest ampacity has to be in the indoor position and this has to be taken into consideration.
RE: Correction factor for cable laying
If Derrated ampacity on conduit > Derrated ampacity on ladder, use first value, if not, use the other
RE: Correction factor for cable laying