Short-circuit calculation on derrated generator

Short-circuit calculation on derrated generator

Short-circuit calculation on derrated generator

(OP)
Hello,

I am calculating the subtransient short circuit currents given a set of 8 generators using ETAP and I would like to know if I should use the rating (kW) under ISO conditions or the rating under SITE conditions (derrating power taking into account the winds and ambient temperature)

P(ISO) = 1305 kW
P(SITE) = 1200 kW (given by vendor)

What do you think?

Regards,
Juan

RE: Short-circuit calculation on derrated generator

The generator reactances are referenced to rated MVA of generator. It has nothing to do with the gas turbine output as such.
Gas turbine outputs are relevant when load flow in a given season or ambient temperature conditions is being performed.

Rompicherla Raghunath

RE: Short-circuit calculation on derrated generator

(OP)
Raghun, thank you for your answer

So, for example

Given the following data:

Generator continuous rating = 200 kVA
Generator Stand By rating = 220 kVA
Prime motor rating (gas motor) = 250 kVA
Derrated motor rating at site = 210 kVA

What number do you think I should enter on ETAP's generator rating for Shortcircuit calculations?

Thanks,

RE: Short-circuit calculation on derrated generator

You have to know what base kVA the reactances are calculated on. It isn't a choice you make. There is only one correct value. If not clear from the data, contact the manufacturer.

RE: Short-circuit calculation on derrated generator

If you don't get the information from the manufacturers, you can perhaps use 200 kVA as the base value, this being the rated continuous value. The possibility of getting wrong is low in this case.

As such by seeing your generator rating, the expected SC level will be so low, the equipment ratings would not be a problem.
Probably for the relay coordination it may be important to have the correct value.

If you have facility to test, you can perform the test and measure the actual value as well!

RE: Short-circuit calculation on derrated generator

If the reactance values are in Ohms the values will not change with a change in the rating.
If the reactance values are in P.U. you must know the KVA base that the P.U. values are based on.
What you give as a continuous rating may be the prime power rating. The prime power rating is most often given and continuous rating and prime rating are not always the same.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Short-circuit calculation on derrated generator

(OP)
Thank you everyone!

From what I have seen in several generator's data sheets, manufacturers never use the word "kVA BASE"

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close