DIN/IEC - Cable Sizing
DIN/IEC - Cable Sizing
(OP)
Hello,
The cable datasheet mentions it is manufactured according to DIN standard. It also mentions IEC standard in the same datasheet. Can I use IEC derating factors for these cables as my company only have IEC standards.
The cable datasheet mentions it is manufactured according to DIN standard. It also mentions IEC standard in the same datasheet. Can I use IEC derating factors for these cables as my company only have IEC standards.






RE: DIN/IEC - Cable Sizing
RE: DIN/IEC - Cable Sizing
The rated current is shown in above standard. However the conversion factor for number of systems[f2] and ground thermal specific resistance, soil temperature and load factor[f1] is in VDE 0276-1000.
IEC 60502-1 does not recommend any current carrying capacity of low voltage cables but IEC 60364-5-52 does.
Let’s take an example of 3*240 mm^2 copper cable XLPE insulated PVC sheathed.
Conditions:90oC conductor temperature, load factor 1[100%] soil resistance 1 K.m/W soil temperature 20oC,number of cable, directly buried[ no conduits].
IEC 60364-5-52 does not make any difference between cable directly buried in soil or in conduit [So does BS 7671].VDE consider 85% for conduits.
The result:
DIN-VDE 428 A
IEC 414 A
It is interesting BS7671 following the same way as IEC the current carrying capacity it is only 382A.
NEC 2014 440 A-but for 0.9 K.m/W[90 oC.cm/W].
RE: DIN/IEC - Cable Sizing
Thanks!
[quote 7anoter4][/IEC 60364-5-52 does not make any difference between cable directly buried in soil or in conduit quote]
Tables B.52.18 and B.52.19 mentions the derating factor for cables buried directly in ground and cables laid in ducts/conduits respectively.
RE: DIN/IEC - Cable Sizing
See Table 52-3 (52H) – Examples of methods of installation providing instructions for obtaining current-carrying capacity item no. 70 up to 73.
RE: DIN/IEC - Cable Sizing