Rustication strips on exposed concrete with discontinuous horizontal wall reinforcement

Rustication strips on exposed concrete with discontinuous horizontal wall reinforcement

Rustication strips on exposed concrete with discontinuous horizontal wall reinforcement

(OP)
Hi everyone,

I was checking out the book "Architectural Detailing: Function - Constructibility - Aesthetics" by Edward Allen and Patrick Rand, and the following detail related to rustication strips on exposed concrete with discontinuous horizontal wall reinforcement (attached, no copyright infringement intended) appeared:

"As recommended by ACI, we discontinue half the horizontal reinforcing bars at each control joint to help create a plane of weakness"

Does anyone know why on earth would one need to create a weakness plane there? I still haven't figured it out. Is it shrinkage related? Because I was told rustication strips are aesthetically related details only.

Thanks and best regards.

RE: Rustication strips on exposed concrete with discontinuous horizontal wall reinforcement

The strip on the upper sketch is not required for shrinkage. It is probably used to hide the pour joint which would otherwise be seen from the exterior.

The lower detail is a plan view near the corner; curtailing half of the horizontal reinforcement and introducing the rustication strips creates a vertical control joint or plane of weakness and is used to prevent unsightly cracking from temperature and shrinkage.

BA

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources