Covert DX coil from R22 to R410A?

Covert DX coil from R22 to R410A?

(OP)
What are the issues with using R410A in a coil originally designed for R22?

My specific application is a 2 circuit 15 ton (2 7-1/2 ton) air handling unit coil.

RE: Covert DX coil from R22 to R410A?

just google, the lot of info and specification of r410A, high pressure refrigerant. system discharge pressure will rise above 600 psig. r22 system designed only to handle 420 psig...also there are differences in thermal properties....

RE: Covert DX coil from R22 to R410A?

Concur with Moideen. I would replace the coil instead of just changing the refrigerant

RE: Covert DX coil from R22 to R410A?

If you replace the evaporator, you should also replace the condenser and compressor. too.

RE: Covert DX coil from R22 to R410A?

Yes good point Willard3. I just assumed you were going to replace the condensing unit and piping and only trying to reuse the evaporator coil. Your filters expansion devices Etc would all need to be replaced as well. And as I recommended so should your evaporator coil.

I've done retrofits from R22 to r407c, which essentially just requires a good flushing of the oil. However, 22 and 410A are not compatible at all with the operating pressures. You really need a whole new system.

RE: Covert DX coil from R22 to R410A?

If the system is old you might also look at the High side lines, if they have any corrosion , they may be marginal.
B.E.

You are judged not by what you know, but by what you can do.

RE: Covert DX coil from R22 to R410A?

(OP)
I would replace the piping with the condensing units.
Do the expansion valves need to be replaced.
No idea on rating of the existing coil. What is the low side pressure for R-410a?

RE: Covert DX coil from R22 to R410A?

RE: Covert DX coil from R22 to R410A?

(OP)
Thanks for the info.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close