Max No. of bank tubes can be pluged
I have water tube boiler and I need to ask about the max. number of tubes in bank tubes (boiler side) can be plugged (due to leakage which difficult to be replaced) that do not cause fail or limit in steam production.
RE: Max No. of bank tubes can be pluged
There is no magic number or percentage. You need to do some calculations based on the design of your boiler and figure out what you can live with.
Agreed with MFJewell - there is no rule of thumb as boilers are engineered for specific design conditions, even package boilers.
And it depends on the distribution of the plugged tubes.
If they are close together then you will run into issues sooner.
thank you for your response, can you mention the reference for such calculations?
Most thermodynamics books would have what you need.
I would look at the impact of the loss of heat transfer area and impact of velocity through the remaining tubes.
Hey MF [et al], maybe you can expand my knowledge...
Is not velocity in tubes generally defined by the head between upper and lower drums, the ID of the tubes, and the triad of quantity of heat transferred / amount of steam generated / percentage phase mixture at the upper / exit ends of the tubes? And since all of the foregoing are more or less fixed for a given firing rate, will not the velocity within the tubes remain relatively unchanged?
Maybe it's just me, but it seems to me that a quite significant number of tubes [and those fairly clustered -thanks, Ed] within a bank of them would have to be plugged before a substantive rise in flue gas exit temperature would occur...
If not, please forgive my ignorance; I've been away from steam for a number of years and have only recently started getting back into it, so if I'm the one getting sharpened, it would be dumb of me to complain about it...smile
CR
IMO, it can be the engineering design question as well as the Plant Maintenance/Inspection issue. Typically in the equipment design, a certain percentage is added to the required design capacity of the Boiler. It can be verified on the data sheet, said about 10% or 15%. From the maintenance history, you may know better about the operation conditions, and then, make a prediction of the remaining life of the equipment and decide a plan of repair or replacement in the future.
SukhpalSingh
Please contact the OEM reg. the number of bank tubes that you can plug.
Also, ensure that there are no roll leaks.
Quote (crshears)
If you are trying to produce the same pounds per hour through less tubes, you are forcing the same mass through less cross sectional area. Therefore the velocity would increase (or you derate the boiler to produce less steam).
This might help .....
http://www.eng-tips.com/viewthread.cfm?qid=429627
There are also ASME Code strength issues to consider when plugging.... detailed here:
https://www.nationalboard.org/SiteDocuments/E-Publ...
In my experience,for firetube boilers, I have heard of a general rule of 5 to 7 percent maximum blocked tubes.
It is important to remember that tube plugging is a temporary fix and that the tube should be replaced at the next schedules outage.
Also it is important to note that boilers in cyclic service will tend to loosen their plugs..!!!
Shell & tube heat exchangers operate under different rules and thermal overdesign is common. As a group they are likely capable of a higher percentage of plugging
http://www.trumboinc.com/sites/559/uploaded/files/...
MJCronin
Sr. Process Engineer
