API 650 Tank - Intermediate Wind Girder design - For Tank with Firefighting system

API 650 Tank - Intermediate Wind Girder design - For Tank with Firefighting system

API 650 Tank - Intermediate Wind Girder design - For Tank with Firefighting system

(OP)
Dear All,

We are designing a Tank with Deluge System (Fire water ring) provided near Top of Tank Shell. The Tank also has an intermediate wind girder (I.W.G) with "T" cross-section located below the firewater ring.Can anyone share your thoughts on the design requirements to be considered on the I.W.G?

In particular, i would like to know, if there is any standard requiring holes to be provided on I.W.G to allow the deluge water to run down smoothly over the Tank shell and to avoid corrosion of I.W.G due to water stagnation.

Comments/thoughts would be appreciated.

Thanks

Arun

RE: API 650 Tank - Intermediate Wind Girder design - For Tank with Firefighting system

See API-650 Section 5.9.3.3.
I assume you don't plan to regularly ignite the tank, so the fire water system is not an issue. The drain holes are so rain and condensation don't accumulate there.

RE: API 650 Tank - Intermediate Wind Girder design - For Tank with Firefighting system

The fire water system shall be tested frequently
Intermediate wind girder obstruct the water to get wet the shell under the girder.

Regards
r6155

RE: API 650 Tank - Intermediate Wind Girder design - For Tank with Firefighting system

(OP)
Thank you bigsmileJStephen & r6155. For your additional info, I also noted another reference in Shell DEP 80.47.10.31, cl. 4.2.6, which reads "Where reinforcing rings, supports, stairs, platforms, nozzles, manholes etc. interfere with the spray patterns or the rundown water layer, additional spray nozzles shall be provided to guarantee complete coverage (including appurtenances)."

Also, in one of a Client specification for Tanks, the requirement given is as follows "Additional water spray ring of tank shall be provided at the nearest level below the tank wind girder.".

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close