Balcony and deck fire sprinklers
Balcony and deck fire sprinklers
(OP)
In a NFPA 13 2013 system with dry heads on balconies and and decks what is the overhang distance that requires a head on the balcony? I have dry sidewall heads with no balcony on the 5th floor only and not on the 6th where the 12" overhang is or on all the floors below .
RE: Balcony and deck fire sprinklers
https://community.nfpa.org/thread/2219
No depth on the overhang specified
RE: Balcony and deck fire sprinklers
903.3.1.2.1 Balconies and decks.
Sprinkler protection shall be provided for exterior balconies, decks and ground floor patios of dwelling units and sleeping units where the building is of Type V construction, provided there is a roof or deck above. Sidewall sprinklers that are used to protect such areas shall be permitted to be located such that their deflectors are within 1 inch (25 mm) to 6 inches (152 mm) below the structural members and a maximum distance of 14 inches (356 mm) below the deck of the exterior balconies and decks that are constructed of open wood joist construction.
RE: Balcony and deck fire sprinklers
https://community.nfpa.org/thread/2219
RE: Balcony and deck fire sprinklers
Maybe if you are going by straight 13, it is four feet, unless 13 has a balcony provision
RE: Balcony and deck fire sprinklers
Balconies, such as those on multistory apartment buildings and that are under 4 ft (1.2 m) in width, do not require sprinkler protection. Balconies more than 4 ft (1.2 m) in width are required to be sprinklered, unless the requirements of 8.15.7.1 are met.
RE: Balcony and deck fire sprinklers
RE: Balcony and deck fire sprinklers
Is this a Building to be built or already built
13r is four stories or less
RE: Balcony and deck fire sprinklers
RE: Balcony and deck fire sprinklers
So who laid out/ designed the system??
RE: Balcony and deck fire sprinklers
RE: Balcony and deck fire sprinklers
Two items
I cannot speak the Canada Building code and requirements,that is a different animal.
Suggest the best person to ask is the designer. That person should be more than happy to tell you why they are there.
Have a great winter
RE: Balcony and deck fire sprinklers
1 - Code supercedes standard. So the IBC/IFC states intermediate landing, then put hose valves on intermediate landing. Both NFPA 14 and IBC/IFC also state to follow the direction of the local AHJ with regard to where these go.
2 - If it is a full 13 system, I believe you only have to do combustible decks when the overhang is >48". However, I would need to confirm that. I think the IBC reference is a subsection to 903.3.1.2 which is the 13R reference.
3 - I am an outside design guy and I always answer field questions. Sometimes the answer may be, I don't know, you need to check with your office for company best practice in that instance. However, in my opinion, it is poor for the designer of the system to not help clarify issues.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...