Can someone point me to a manual or any other design aids for analysis of bolted angle connections. In my case, I am bolting a steel angle directly to a CMU wall - the angle will be oriented horizontal leg up, which will the act as a cantilever to support ~2 kip load (which comes from a 3" wide steel stair stringer that will bear on top of it). I have previously seen engineers completely discount any tension load created by the moment, and design the bolts as being purely in shear - naturally I am wondering how safe this is... Also, I imagine there is prying action, and if so, how should it be taken into account. Thanks!
Can someone point me to a manual or any other design aids for analysis of bolted angle connections. In my case, I am bolting a steel angle directly to a CMU wall - the angle will be oriented horizontal leg up, which will the act as a cantilever to support ~2 kip load (which comes from a 3" wide steel stair stringer that will bear on top of it). I have previously seen engineers completely discount any tension load created by the moment, and design the bolts as being purely in shear - naturally I am wondering how safe this is... Also, I imagine there is prying action, and if so, how should it be taken into account. Thanks!






RE: Cantilevered bolted angle connection design
- in general, the tension on the anchor should not be ignored as a combined load is usually what governs.
- there are situations in which the angle can be considered a flexural extension of the stringers in which case it may indeed be appropriate to consider shear only. We'd need to understand the details of the connection in order to ascertain that though.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: Cantilevered bolted angle connection design
Dik
RE: Cantilevered bolted angle connection design
RE: Cantilevered bolted angle connection design
RE: Cantilevered bolted angle connection design
Dik
RE: Cantilevered bolted angle connection design
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: Cantilevered bolted angle connection design
If they are welded together so that the angle really is just an extension of the the vertical wall of the HSS as KK says.
RE: Cantilevered bolted angle connection design