Earth cable sizing calculations

Earth cable sizing calculations

Earth cable sizing calculations

(OP)
Hello friends,


Can anyone explain how earthing cables sizes can be calculated to comply with BS7671 please? any supporting documents or materials would be appreciated.

Thank you

RE: Earth cable sizing calculations

For applications where the earthing conductor size isn't explicitly called out you can use the adiabatic equation with appropriate factors. Have a look at http://www.napitonline.com/downloads/CP%203%2007%2... for a starter. I think this article is from an earlier edition of the wiring regulations - probably the 16th Edition - but the method is still valid. Google BS 7671 adiabatic equation and have a read of some of the hits.

RE: Earth cable sizing calculations

I think you speak about Regulation 543 Protective Conductor.
If it is known the presumable maximum short circuit phase-to-ground and the fault clearance time [of the protection device] you can use the formula 543.1.3 S=sqrt(I^2*t)/k
If the live conductor is known then see Table 54.7.
If you want to know how this above formula was deducted you have to start with the assumption that all the heat produced in the conductor remains in conductor and is not exhausted outdoors.
If R.I^2*dt it is the energy loss and c.Vol*d*dT it is the heat deposited in the conductor where c it is heat capacity of the conductor material, d it is material specific gravity, Vol it is the conductor volume and dT it is the increasing temperature, R=ro*[1+a*(T(t)-T(o)]*length/S where ro it is material resistivity and a it is the resistance temperature factor then:
ro*(1+a(T-To)*length/S*I^2*dt=c.d.length*S*dT.
By integrating you’ll get the IEEE 80/2000 formula 37:
I=Amm^2√{[TCAPx10^-4/(tc*ror*ar)]xln[(Ko+Tm)(Ko+To)]}
where:
I is the rms current in kA
Amm^2 is the conductor cross section in mm2
Ko= 1/αo or (1/αr) – Tr in °C
Tm is the maximum allowable temperature in °C
Ta is the ambient temperature in °C
Tr is the reference temperature for material constants in °C
αo is the thermal coefficient of resistivity at 0 °C in 1/°C
αr is the thermal coefficient of resistivity at reference temperature Tr in 1/°C
ρr is the resistivity of the ground conductor at reference temperature Tr in μΩ-cm
tc is the duration of current in s
TCAP is the thermal capacity per unit volume from Table 1, in J/(cm3 • °C)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources