(OP)
Let's say I have 3" of 5000 psi concrete (3" topper of a 6" thick deck), such that le=da=3". I want to put plates on both sides and bolt through the concrete with 3/4" A36 rod to connect the plates. The closest edge distance is 20.5" (ca1). I am using ACI 318-14. Avco (17.5.2.1) is very large because of the large edge distance and Avc is very small because of the 3" thickness. So my Avc/Avco = 0.098. Vb (17.5.2.2) is equal to 52.5 kip [9*sqrt(f`c)*ca1^1.5 -OR- 7*(le/da)^0.2*sqrt(da)*sqrt(f`c)*ca1^1.5]. My Vcb ends up being 5.12 kip. This seems pretty small for such a large edge distance. Am I missing something? Am I shooting myself in the foot by only using the continuous 3" thickness of the topper? There is WWM in the topper, should I be including that somehow?

It is a little crude since it is preliminary, but below is my math.


Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant

RE: Thru-Bolt Concrete Anchor Shear Breakout Capacity

(OP)
I see that through-bolts are excluded from Chapter 17 (17.1.2) thanks to reading this post: http://www.eng-tips.com/viewthread.cfm?qid=248052

So now my question is, how do you check the shear capacity of a through-bolt?

Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant

RE: Thru-Bolt Concrete Anchor Shear Breakout Capacity

usually if possible we use a shear key for the shear force and not the bolts
unless the shear force is 'small'



best regards
Klaus

RE: Thru-Bolt Concrete Anchor Shear Breakout Capacity

(OP)
klaus,

We are tieing a construction elevator to the building's floor. We have no control over the concrete, but we do know what it is. I have about 10.72 kip of resultant shear (9.42 kip towards 20.5" edge, 5.13 kip parallel to edge) and my client's typical anchorage is (2) 3/4" A36 rods through sandwiched plates. Tension is only 1.7 kip. Threaded rods are 6.5" apart and the parallel-to-edge force has a line of action through both bolts. AISC bolt shear analysis tells me A36 rods are good for 11.5 kip total [5.75 kip per rod], so I don't have enough shear capacity remaining to pretension the bolts to gain frictional resistance. This leaves me with relying on the bolts to bear on the concrete. I can check the concrete shear capacity (conservatively assumed unreinforced) as shown below.

I know concrete is LRFD, so the below is a quick check of my ASD load vs. an ASD allowable concrete shear using the known AISC LRFD:ASD relationship between omega and phi.

Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources