Change to pier tie spacing requirement, ACI 318-11 to ACI 318-14

Change to pier tie spacing requirement, ACI 318-11 to ACI 318-14

Change to pier tie spacing requirement, ACI 318-11 to ACI 318-14

(OP)
ACI 318-11 section 7.10.5.7 states, "Where anchor bolts are placed in the top of columns or pedestals, the bolts shall be enclosed by transverse reinforcement that also surrounds at least four vertical bars of the column or pedestal. The transverse reinforcement shall be distributed within 5" of the top of the column or pedestal and shall consist of at least two No 3 or 3 No 3 bars."
I`m also accustomed to seeing these tightly spaced ties just below the bottom of two way flat slabs in multi story concrete construction.

I`m dealing with a situation where I have piers/pedestals adjacent to my perimeter wall, so that all of my steel bears at the same elevation while the footing steps down for frost protection. The contractor cast all of the piers too high and is now chipping them down to the proper elevation. In the process, he's chipping out these added ties.
I think it's pretty clear that these ties are required, however, this provision seems to have been eliminated from ACI 318-14.

Does anybody have any insight into why this provision was removed? Previous conversations indicate that these ties have their roots in the seismic requirements of UBC beginning with ACI 318-02, but I can't find anything about these ties in the seismic section either.
http://www.eng-tips.com/viewthread.cfm?qid=143033
Have these changed to a design requirement rather than a prescriptive requirement?

As always, thanks!

RE: Change to pier tie spacing requirement, ACI 318-11 to ACI 318-14

The provision has been moved to 10.7.6.1.6 in ACI 318-14. The transition keys on this page are useful for cross-referencing provisions between 318-11 and 318-14.

RE: Change to pier tie spacing requirement, ACI 318-11 to ACI 318-14

(OP)
Great reference!
Thanks Deker.

RE: Change to pier tie spacing requirement, ACI 318-11 to ACI 318-14

Excellent! Thanks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources