Siemens 7SJ64 SFC feeder trip

Siemens 7SJ64 SFC feeder trip

Siemens 7SJ64 SFC feeder trip

(OP)
Hello all,

in our 6.6kV switchboard we have a transformer feeder which feeds a 4.4MW static frequency converter. During starting, the relay tripped in earth fault in 300ms. When we retrieved the disturbance records from relay, the peak waveform is shown as attached.
We suspect in B phase the firing of negative wave didnt happen in SFC which caused earth fault to trip. Because if you see in waveform the negative peak of B phase is exactly in earth fault current.

Thanks,
Vijay

RE: Siemens 7SJ64 SFC feeder trip

I expect the SFC transformer to have 'Delta' connection on 6.6kV side. If true, the earth fault protection relay on 6.6kV side cannot see zero sequence currents or triplen harmonics on the SFC side.
Do you have CBCT in the SFC transformer feeder? If so, check whether it is sized / placed correctly.
Most likely, the problem is CBCT sizing/installation and as a result, the spurious currents appear in the CBCT secondary during transformer enegisation, to cause protection maloperation.

Rompicherla Raghunath

RE: Siemens 7SJ64 SFC feeder trip

(OP)
Hi Raghu,

This earth fault is calculated current by the relay based on 3 phase currents, not from CBCT.

Thanks,
Vijay

RE: Siemens 7SJ64 SFC feeder trip

Hi Vijayapandiyan!
If it is not CBCT, what is the phase CT ratio and what is the earth fault protection setting in the relay?
What is the neutral earthing arrangement for the 6.6kV incoming transformer source! Is it not resistance earthed, if so, what is the NER current rating?
Is the 7SJ64 relay with 2 or 1 in the 7th position of its MLFB?
Is neutral CT on Secondary side of SFC transformer connected to this relay in your scheme!
If the earth fault protection is based on phase CTs, there is a possibility of maloperation during transformer energisation. It is recommended to enable 2nd harmonic block 97sj64 has the feature) for this protection in the relay.

Rompicherla Raghunath

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources