I've been setting up a calculation following the heat transfer calculations outlined on pages 4.3 & 4.4 of the ashrae fundamentals handbook (2017). I've been using their example to check my spreadsheet before adapting for my actual calculation.
The problem is I can't seem to get all the numbers to pan out. I was wondering if someone else could crosscheck for me to see if it is me or the document that is wrong.
I don't really want to post the actual text for copyright infringemnt reasons, but I am getting different answers for both R2 & R3.
The stated results are
R2 = 3.37*10^(-5) h.degF/Btu
R3 = 0.254 h.degF/Btu
The results I am getting are
R2 = 2.82*10^(-6) h.degF/Btu
R3 = 0.021 h.degF/Btu
In both cases I am out by a factor of 12 which is obviously a feet-to-inches conversion, but in the context of how the information is presented this does not make sense.
thanks in advance.
thanks in advance.
RE: Ashrae fundamentals calculation - heat transfer off insulated pipe.